10/2 wire question

   / 10/2 wire question #51  
I'm not gonna' touch anything in the fuse panel in this rented house, as far as what you guys are telling me about electrical codes,I think that the owner of this house hired a cheezy electrician,because no where is there any conduit to these electrical boxed recepticals beside the main panel which is a big mess of wires,so I guess I'm living in a death trap so to say,anyhow I'm gonna' get hold of a Lincoln rep and ask him why his company sell a 110volt welder that infact needs a 20 amp service to run it proper and it's equipped with a normal 15 amp 3 prong plug,I've read enough insaults to last me a life time,some about the way I type,I know how to it's just that I wanted to creat a sort of stye of my own,I've seen people do it like this<> or-------etc I like it like this.......so bite me!....and I'll do it any way I like with typing out a post... it's a free country or is it?Hmmmmmm lets think about that for awhile...thanks to the guys that know what they're talkin' about... I was listening!!!!.....the others????? unsigned this time round you know who I am>>>>>>>>>>>>>

No insults were given. You can not run 20 amps on 14 ga wire plain and simple. A electrician will tell you you will need 12 ga wire for 20 amps for most run lengths. We are trying to keep you safe and your landlord happy.

As for no conduit its not required in my part of the country. Not sure where you live but if you were to get a electrician in to check it all out you would have the right answers and then a legitimate fight with your landlord.

Chris
 
   / 10/2 wire question
  • Thread Starter
#52  
"Yep" I know that the bare copper wires are altogether in one place in the service panel(main panel)...and the white/neutrals are altogether at the bottom...my buddy the electrician pointed this out to me as well... matter of fact he phoned me tonight about something else, and I mentioned to him about connecting my 20 amp breaker,but he's really busy at his shop,but he's confident that I can do the work and if I'm sure I want him to check out what I've done he will,and won't charge me this time around,it's really nice to have good friends in the trade business,anyhow Captain thanks ever so much for your interest and input, like I mentioned I'll report back on the performance for sure, but in the meantime take care..... Ampa :):thumbsup:
 
Last edited:
   / 10/2 wire question #53  
No insults were given. You can not run 20 amps on 14 ga wire plain and simple. A electrician will tell you you will need 12 ga wire for 20 amps for most run lengths. We are trying to keep you safe and your landlord happy.



Chris
As of Today, 05:23 PM, he has that covered (12/2)....
 
   / 10/2 wire question
  • Thread Starter
#54  
Chris, I've never ever had any problems with you....... my comments were not directed at you at all,I always enjoy reading your many answers to other peoples questions and trust them always to be right on the money,anyhow I think you just came in on the tail end of this whole mess,but I assure you everything is quite under control to the experts,I know what you were telling me,I mentioned the service panel bein' somewhat a mess, but my friend Don the electrician will check it out and if he thinks it's not done to standards or code,he'll bring it to my landlords attention and make certain it's done to standards, or put a yellow tag on it,condeming it,and make certain the electrician that originaly wired this house comes back to correct it ASP,or if the lanlord wants Don to do it properly, I told my friend Don,to me it looks like a rats nest,but what do I know, least I'll get a second opinion from a pro.... many thanks to u Chris on this rather long and winded and confusing Lincoln 125 volt issue...take care.....Ampa...:)
 
Last edited:
   / 10/2 wire question #55  
No question, the best advice is a licensed electrician. Notwithstanding, here is how I understand the OP's issue.

He has a 120 volt welder. When he plugs it into a "normal" outlet (15 ampere) it "blows the fuse" (i.e., trips the overcurrent device). So, he has determined that a higher capacity, 20 ampere, overcurrent device (breaker) should be installed on the circuit and the wire from the breaker box to the outlet should be sized accordingly, say 10 ga copper.

Inasmuch as the circuit is 120 v, 10-2 with separate ground is reasonable. Normal configuration would be two insulated solid conductors, one with white insulation and one with black insulation, and a bare copper ground wire.

For some reason, he bought/was sold 10-2 red/black with bare ground. There would be less confusion if the OP simply would buy a length of the std configuration cable, which is not expensive for a short length. Either return the other, sell it on Craig's list, or frame it and chalk it up to a learning experience.

With the correct cable, in the box: black to new 120v 20A breaker, white to neutral bar (where there are other whites) and bare to neutral bar where other bare wires are.

Now, route the cable (properly) to the outlet. This should be a single outlet in a work box, flush or surface. The outlet should be NEMA 5-20R (see attached jpg) with the black wire attached to the darker/copper colored terminal, the white to the lighter/silver colored terminal, and the bare wire to the green terminal (and the workbox grounding screw if it's a metal workbox).

Because this 5-20R can accommodate either a 20A (i.e. NEMA 5-20P) or an ordinary 15A plug, no need to do anything to the welder plug (assuming it is in good shape).

I believe the OP more or less knew what had to be done (new, bigger breaker and cable to the receptacle) but didn't/doesn't quite understand how to do it and got further confused by acquiring the "wrong" wire. Perhaps as others have said, the "wrong" wire could be used my using the red as white and marking appropriately at each end...but, why bother?

What was unsaid, above, is the need to replace the receptacle in the workbox to the NEMA 5-20R (see jpg).

That said, get an electrician.
 

Attachments

  • NEMA 5-20 P and R.jpg
    NEMA 5-20 P and R.jpg
    127.8 KB · Views: 147
   / 10/2 wire question #56  
No question, the best advice is a licensed electrician. Notwithstanding, here is how I understand the OP's issue.

He has a 120 volt welder. When he plugs it into a "normal" outlet (15 ampere) it "blows the fuse" (i.e., trips the overcurrent device). So, he has determined that a higher capacity, 20 ampere, overcurrent device (breaker) should be installed on the circuit and the wire from the breaker box to the outlet should be sized accordingly, say 10 ga copper.

Inasmuch as the circuit is 120 v, 10-2 with separate ground is reasonable. Normal configuration would be two insulated solid conductors, one with white insulation and one with black insulation, and a bare copper ground wire.

For some reason, he bought/was sold 10-2 red/black with bare ground. There would be less confusion if the OP simply would buy a length of the std configuration cable, which is not expensive for a short length. Either return the other, sell it on Craig's list, or frame it and chalk it up to a learning experience.

With the correct cable, in the box: black to new 120v 20A breaker, white to neutral bar (where there are other whites) and bare to neutral bar where other bare wires are.

Now, route the cable (properly) to the outlet. This should be a single outlet in a work box, flush or surface. The outlet should be NEMA 5-20R (see attached jpg) with the black wire attached to the darker/copper colored terminal, the white to the lighter/silver colored terminal, and the bare wire to the green terminal (and the workbox grounding screw if it's a metal workbox).

Because this 5-20R can accommodate either a 20A (i.e. NEMA 5-20P) or an ordinary 15A plug, no need to do anything to the welder plug (assuming it is in good shape).

I believe the OP more or less knew what had to be done (new, bigger breaker and cable to the receptacle) but didn't/doesn't quite understand how to do it and got further confused by acquiring the "wrong" wire. Perhaps as others have said, the "wrong" wire could be used my using the red as white and marking appropriately at each end...but, why bother?

What was unsaid, above, is the need to replace the receptacle in the workbox to the NEMA 5-20R (see jpg).

That said, get an electrician.

Good summary, Joe
 
   / 10/2 wire question #57  
Ampa, since the other questions have been answered many times over, figured I'd say something about the plug on your welder

I have a small FCAW welder that has the typical 15A/125V plug on the end (NEMA 5-15p). The manual says that a 15A circuit is fine if I use the lower heat settings, but that I need 20A if I use the highest. Since I have a dedicated 20A available, I just use it.

I would imagine this is similar to your situation - and that is probably what Lincoln will tell you.
 
   / 10/2 wire question
  • Thread Starter
#58  
Although I have'nt connected anything as of yet,because ol' man winter is still with us in cold country Canada, I'm in no hurry to do any welding outside as of yet,I will get back to everyone as promised on how this Lincoln works on a 20 amp circuit,I have learned a whole lot,and appreciate all the sound advice givin' to me,I now know you all gave me,the best information available,I took some the wrong way,and bein' stubborn is no excuse to how I reacted,I'm ever so glad to belong to such a great forum and such a good bunch of people/guys.... as always take care everyone....Ampa :thumbsup:
 
   / 10/2 wire question #59  
Steve, Keep in mind that finer wire (or stranded as it's called in the Trade) is a plus, but it's more about the type of insulation used on the wire and the listed use of the cable or cord.... Rubber cords are often listed to carry more Amps then cables listed to be concealed in walls. Keep in mind that cords can dissipate heat better in the open. That same cord installed in an insulated wall can build up heat and create a fire hazard... One should also consider wire size, load and distance to prevent Voltage Drop...


I had to get one shot in at the regulators, thats par for the course isn't it?

Steve
I think you two have done a good job summing it up and weeding out the uncertainties that have gotten mixed in. :confused2:
As far as I can tell the OP just wants to run a 110V welder outside thru a 10/2 w ground ext cord. There is a single duplex outlet right beside the service panel. This outlet is served by a 15A breaker thru a 2' long exposed 14ga romex cable that serves nothing else. He has posed a plethora of options that have taken the thread global, but among them is just putting a 20A breaker on that single feed. Definitely out of code, but definitely adequate in the special circumstance. The other easy option is to rewire that duplex with 12ga while installing the 20A breaker. The only further upgrade I see that code would require would be a 15/20A duplex [GFI duplex or breaker if wet] in place of the generic duplex already there. With the dwelling owners permission it wouldnt cost much with his electrician friend helping ... and then have it inspected to cover.
larry
 
   / 10/2 wire question
  • Thread Starter
#60  
Long Story Short....the landlord just gave us 120 days to move as he says he's renovating the whole house due to my complaining about the electrical panel and other things,so I won't be able to give any info on the set up,may even have to sell my ol' Iseki tractor, unless I can rent a townhouse for about the same rent as here,rents are goin' sky high up around this area,buyin; a house for me and my lady is not a good option,as I'm too old to get a morgage,so as it stands,I may be out in the street or livin' out of my van,I'm not just kidding,anyhow guys I'd hate to lose my tractor that I've put so much time and money into "NO" guys it was my own fault for complaing,so I must now live with it,I hope that I can still come back to chat,even though I maybe won't have a tractor,but the memories I'll cherish,take care all,Ampa
 

Tractor & Equipment Auctions

John Deere 5090E Tractor with Loader Prep Package, 2 Rear Remotes, Warranty Until 2028 (A53472)
John Deere 5090E...
2008 DOOSAN G25 GENERATOR (A52472)
2008 DOOSAN G25...
2016 R&R Products 331 LP Reel Mower (A51691)
2016 R&R Products...
2013 Mack GU813 Roll Off Truck, VIN # 1M2AX13C1DM019680 (A51572)
2013 Mack GU813...
2019 Toyota Corolla Sedan (A51694)
2019 Toyota...
2003 JOHN DEERE 350D OFF ROAD DUMP (A51246)
2003 JOHN DEERE...
 
Top