Thank you. I stand corrected.No, that's not the way it works if properly wired. CurlyDave is correct.
When you have equal loads on both sides, the neutral current is balanced out and the neutral has zero current. If the loads are unbalanced, then the neutral will only carry the difference. For example, one side has a 20 amp load and the other side has a 15 amp load, the neutral will only carry 5 amps.
As long as you actually have 220 at the end, it's fine. Now if you wired it wrong and connected both hot wires to the same side of the feed, then yes, your neutral current would be too high, but you would have zero voltage between the two hot wires and 110 to ground on both.
Ken
Thanks everyone. Fantastic advice.
It is a copper wire, the jacket states Direct Burial 2008 manufacturing date.
The jacket also states 10-3 and there are only 3 wires. I guess I have been working with ROMEX too darn long cause I always thought 10-3 meant 2 hots, a Nuetral and a ground. This stuff does not have the 4th wire that I expected.
That said, I am going to cobble from some scrap (wire that the previous Meth addict owner used to run his operation with) to create my ground. Not ideal (Code) but it will work.
And that being said, Could I just create a ground by putting a ground post in where these wires come out? I guess it would create a ground loop? (2 Hots, a Nuetral and then tying to the 6 ft grounding rod).
Carl
I just finished wiring a new house, and with #6 and larger all that is available is stranded. I think you will be fine with stranded. It is easier to handle, not as stiff as single strand,
There is no rule against romex in conduit so long as you don't exceed the fill requirements and so long as you are not in a "wet" location. That's an old wive's tale.
Maybe, but in 1984 I had an inspector for the state of Ohio, tell me I could not run one 12/2 Romex wire through 1/2 conduit, in a commercial building.
He said, if I did not remove the outer jacket, he would pass it.
He was cutting us some slack by letting us run a few Romex wires through the attic without conduit. So, I did not argue.
He insisted the same wires that ran down the inside of the finished walls, be in conduit. :confused2: