10-3 Direct Burial wiring question

   / 10-3 Direct Burial wiring question #31  
Maybe, but in 1984 I had an inspector for the state of Ohio, tell me I could not run one 12/2 Romex wire through 1/2 conduit, in a commercial building.

He said, if I did not remove the outer jacket, he would pass it.

He was cutting us some slack by letting us run a few Romex wires through the attic without conduit. So, I did not argue.

He insisted the same wires that ran down the inside of the finished walls, be in conduit. :confused2:

Sorry, I meant to say: He said, if I did not remove the outer jacket, he would NOT pass it.
 
   / 10-3 Direct Burial wiring question
  • Thread Starter
#32  
Tomorrow I will be trenching (potato plowing) my water and power to the new garden / greenhouse.

I recieved a few requests for a jacket picture so here it is...

If you can't read it it says.. NEXANS ULTREX XL 3/C 10 AWG TYPE TC-XHHW-2 (UL) e64956 F SUN RES DIR BUR 600V

Thoughts?
 

Attachments

  • Direct Burial.jpg
    Direct Burial.jpg
    461.8 KB · Views: 142
   / 10-3 Direct Burial wiring question #33  
I think you will find that what you have is called " Tray cable".. good stuff go ahead and burry it,,
 
   / 10-3 Direct Burial wiring question #34  
Wire is fine for direct burial. But, for 2-20 circiuts you'll need a 4th wire. Personally, I'd just run a single 20A circuit off that and call it good. Watch your depth. You can get by @ 12" if the cable is GFCI protected at the source.


WDO
 
   / 10-3 Direct Burial wiring question #35  
Wire is fine for direct burial. But, for 2-20 circiuts you'll need a 4th wire. Personally, I'd just run a single 20A circuit off that and call it good. Watch your depth. You can get by @ 12" if the cable is GFCI protected at the source.


WDO

12" is a good depth to accidentally dig it up. :(
 
   / 10-3 Direct Burial wiring question #36  
I use a Klein (part # 1005) crimper for the crimp connectors you would need. I've seen too many crimps fail when a cheapo "six in one" tool was used. They are about 20+$ at DIY store. We use all stranded wire (quite often tray cable wire) at my plant and I've put thousands of crimps on.
 

Tractor & Equipment Auctions

2020 TAKEUCHI TL 12V-2 (A52472)
2020 TAKEUCHI TL...
2025 25ft. 800Amp Extra HD Booster Cables (A51692)
2025 25ft. 800Amp...
2018 KENWORTH T680 TANDEM AXLE SLEEPER TRUCK (A52576)
2018 KENWORTH T680...
CONTACT INFO (A53084)
CONTACT INFO (A53084)
WE DO NOT GUARENTEE HOURS UNLESS WE SAY SO!!! (A50775)
WE DO NOT...
DROME EXCAVATOR SLIDE ATTEHMENT (A50322)
DROME EXCAVATOR...
 
Top