110V off 220V circuit

   / 110V off 220V circuit #1  

dieselscout80

Veteran Member
Joined
Nov 17, 2007
Messages
2,206
Location
South Carolina
Tractor
New Holland TC45DA
I need to temporarily pull 110Vac off a 220Vac circuit for lights. I know that 220Vac with three total wires is two 110Vac legs and a ground. I think I can attach the black from the 110Vac to one of the 220Vac legs to get 110V, but what does the neutral (white wire) of the 110Vac circuit attach to?

Is this safe to do for lights?
 
Last edited:
   / 110V off 220V circuit #2  
There should be 3 wires for 220vac

black hot 1
red hot 2
white neutral
(maybe green for grounD)

If you connect to either black or red, and use white as neutral you will be OK

white to silver screw
black OR red to brass screw
 
   / 110V off 220V circuit #3  
No. You can only split a 220 circuit into two if it has a neutral. The ground is there for safety and can't be used as a conductor. You could wire up a pair of lights in series so they will run off 220V.

Edit: The original poster sounds like he has a 220 only circuit like a baseboard heater.
 
   / 110V off 220V circuit
  • Thread Starter
#4  
No. You can only split a 220 circuit into two if it has a neutral. The ground is there for safety and can't be used as a conductor. You could wire up a pair of lights in series so they will run off 220V.

Edit: The original poster sounds like he has a 220 only circuit like a baseboard heater.

Its a window AC unit plug.

Ok it sounds like that it is NOT possible to due unless the 220Vac circuit has four wires (black, red, green and white{neutrual}) and mine doesn't.

Thanks
 
   / 110V off 220V circuit #6  
If there is not anything else on the circuit (and there shouldn't be) you could remove the wires from the double pole breaker in the electrical panel and wire one of them to a single pole breaker and the other to neutral. The circuit would now be 110V.

I will caution you that if you are not experienced working in an electrical panel, please hire an electrician.
 
   / 110V off 220V circuit #7  
If the temporary light that you are using has two prongs on the cord end then you do not need a grounded outlet and using one of the hot leads and the neutral for your outlet would be just fine. I would recommend that you locate an ungrounded outlet for this temporary set up then there is no confusion as to whether or not the outlet is grounded and should only be used with ungrounded appliances (i.e. floor lamp,table lamp,double insulated tools). Yes you can still buy this type of receptacle even at home Depot.
 
   / 110V off 220V circuit
  • Thread Starter
#8  
If the temporary light that you are using has two prongs on the cord end then you do not need a grounded outlet and using one of the hot leads and the neutral for your outlet would be just fine. I would recommend that you locate an ungrounded outlet for this temporary set up then there is no confusion as to whether or not the outlet is grounded and should only be used with ungrounded appliances (i.e. floor lamp,table lamp,double insulated tools). Yes you can still buy this type of receptacle even at home Depot.

I don't follow?? Where would the neutral hook to on the 220Vac circuit?
 
   / 110V off 220V circuit #9  
No. You can only split a 220 circuit into two if it has a neutral. The ground is there for safety and can't be used as a conductor.

Yep, if there is no (white) neutral wire, don't pass go. :thumbsup:

Now, as kfu4da said, there is a good possibility of rewiring it temporarily for 115 vac., but he better be sure how everything is connected, and what the wires are connected to, before doing that.
 
   / 110V off 220V circuit
  • Thread Starter
#10  
Yep, if there is no (white) neutral wire, don't pass go. :thumbsup:

Now, as kfu4da said, there is a good possibility of rewiring it temporarily for 115 vac., but he better be sure how everything is connected, and what the wires are connected to, before doing that.

Thats what I thought.
 

Tractor & Equipment Auctions

New/Unused 14ft Bi- Parting Iron Gate (Deer Design) (A44391)
New/Unused 14ft...
2010 Mitsubishi Fuso FE84D Box Truck (A44571)
2010 Mitsubishi...
1996 Mack RD688S Dump Truck, VIN # 1M2P267C2TM025082 (A44391)
1996 Mack RD688S...
INOP/NON RUNNING 2016 International CT660 Truck, VIN # 3HTJGTKT6GN292959 (A44391)
INOP/NON RUNNING...
(3) Goodyear 10R 22.5 Tires (A44391)
(3) Goodyear 10R...
2014 Chevrolet Express 2500 Cargo Van (A44571)
2014 Chevrolet...
 
Top