The bare copper wire going down to the plug looks to be of the same size as the other three with the exception that it is solid and the red, black and white are braided. The bare copper is in the same wire jacket as the rest.
The 240 circuit is #6 wire from the 50A breaker to the plug below. The larger three red, black and white wires at the upper part of the box is the feed from the 100A main over at the house.
Since the #6 white seems to be only attached at the neutral, I know it isn't inside the plug box, should I just leave it alone?
Thanks for responding.
CORRECTION: The solid bare copper ground wire is about or more than half the diameter of the other three braided wires, compared copper to copper.
sorry I just now saw this reply! UNHOOK the white wire in the breaker box, shorten and cap securely with a wire nut. there should never be a wire hooked on source end that dead ends somewhere other then caped in a covered box. my guess is it has been cut off where wires exit the outer jacket.
1. For peace of mind and since it appears to be doing nothing, should I detach the white wire at the neutral bar and cap it off?
2. Should I pull the existing complete #6 four wire out (it's only about three feet long) and replace it with #6 hot black, hot white and ground green, following the exact sub panel connection path as the existing hot red, hot black and bare copper ground?
3. Leave it as is?
Again, thanks all, just want it to be safe and right for the three pronged connection welder.
#2- is wall sheet rocked or otherwise covered? if so leave it in there, if anything is holding it in place ,screw clamps at boxes, wall staples they will cause issues and even though it is only 3' it is required to be stapled/secured