3 phase converted to single phase

/ 3 phase converted to single phase #1  

yanmars

Veteran Member
Joined
Nov 29, 2009
Messages
1,136
How difficult/expensive to convert a 3 phase propane generator to single phase for home use? Would the transfer switch need to be changed also?
 
/ 3 phase converted to single phase #2  
How difficult/expensive to convert a 3 phase propane generator to single phase for home use? Would the transfer switch need to be changed also?
You need to derate the output. For instance if its a 20 kw the single phase output will be about 14 KW. Its not done very often. Some generators can be rewired in the stator can, some can’t. Need to check with manufacturer
 
/ 3 phase converted to single phase #3  
Check with the manufacturer. I am not sure you need to do anything. If it is a 230V 3 Phase generator, you maybe able to just connect to two of the three wires to use for single phase power. This is what I would do coming off a 3 phase transformer. I am just not sure it is OK to do from a generator?
 
/ 3 phase converted to single phase #4  
Check with the manufacturer. I am not sure you need to do anything. If it is a 230V 3 Phase generator, you maybe able to just connect to two of the three wires to use for single phase power. This is what I would do coming off a 3 phase transformer. I am just not sure it is OK to do from a generator?
Ive seen it done, but its not recommended. Hard on an alternator. Not the same as a transformer. Better 3 phase units have wiring in stator can that can be swapped around to get single phase
 
/ 3 phase converted to single phase #5  
Thanks. I wasn't sure if it would hurt a generator to have one phase not being used.
 
/ 3 phase converted to single phase #6  
Do you plan to convert the generator to single phase or just use one phase of the three? The Cycle Stop Valve url has no bearing. If you elect to use a single phase of the three be advised that the single phase voltage may not be what you expect. You should consult with an electrician for your own safety and that of the equipment..
 
/ 3 phase converted to single phase #7  
... If you elect to use a single phase of the three be advised that the single phase voltage may not be what you expect. You should consult with an electrician for your own safety and that of the equipment..

Ayup.
 
/ 3 phase converted to single phase
  • Thread Starter
#8  
It is a Kohler unit if that helps any.
 
/ 3 phase converted to single phase
  • Thread Starter
#10  
Model 20 RZ
 
/ 3 phase converted to single phase #11  
I cant find any wiring diagram on the 20RZ, But I did find one on the 12RZ. It shows that it had a 12 wire stator that can be rewired to single phase pretty easily. But it will still derate generator by 33%. So a 20 kw unit will be a put 14 KW output.

But it should work.
http://www.sailing.com.br/loja/manual/17e22op.pdf
 
/ 3 phase converted to single phase
  • Thread Starter
#12  
Thanks for that information
 

Marketplace Items

New/Unused Landhonor Adjustable Gantry Crane (A61166)
New/Unused...
2013 International WorkStar 7400 4x4 Altec AM650 50ft Material Handling Insulated Bucket Truck (A59230)
2013 International...
2023 HarbinGer V3 Plus S/A Towable Light Tower (A60352)
2023 HarbinGer V3...
2024 JCB 35Z (A60462)
2024 JCB 35Z (A60462)
17307SFL (A61569)
17307SFL (A61569)
2018 CATERPILLAR 236D SKID STEER (A62129)
2018 CATERPILLAR...
 
Top