The PA 300 will work with that 3 phase power, and pull less amps. Use the red leg for the high leg (high voltage).
Thanks. Now, I know.I've been over, in and under 540, 750 and 860MW nuclear powered steam turbine generators and their support systems for 23yrs. As a Control Tech, Fire Captain and Radiation Protection Green Badge.
Canada is 60 HZ for sure but there are companies that bring oodles of used machine tools over from Europe to sell here.
Ron,In my recollection of past history what you have is what is called an open delta power distribution. This is a system very seldom used anymore. It was used by power companies to provide 3 phase power for motor loads where the distribution system in the area was single phase, like predominately residential areas. I first encountered this in Phoenix AZ back in the 50s when Air conditioning was becoming high demand in homes. That was their short term solution till revenue for more power paid for changing the distribution systems to three phase primary. At that time 3 phase compressor motors were half the price of single phase and were much more efficient, hence this solution.
Open delta is derived from single phase using only 2 transformers. The so called "wild leg" by code could only be used for the third phase (3rd conductor) of a motor circuit. That conductor had to be a unique color from all the others so it could be readily identified. The motor circuit could not be part of the distribution panel that was required to only single phase. We bus tapped the other two conductors in a gutter ahead of the panel to insure separation. It was a grossly unbalanced system electrically and raised havoc with the newly emerging TV sets and radios. A lot of these setups rapidly were overloaded as more AC units were added to that second transformer. The power company loaded them till they blew up and then replaced with a bigger one.
You probably will never see power companies doing this today. I looked into it once for a 15 HP motor and they said it was my problem to solve with an electrical contractor on my side (secondary). We did the open delta just for the motor. By the way the open delta provides only 60% of the power for the same KVA as a delta or Y connected transformer bank.
This is all recollection from my early years as an Air-conditioning technician in Phoenix.
Ron