Coffeeman - The NEUTRAL (the white wire) goes through the GFI breaker as well as the hot wire (usually black or red). The neutral is bonded to ground at the main panel (which may or may not be the panel the GFI breaker is in). The ground wire (bare or green) does NOT go through the GFI breaker. If the GFI breaker trips when you connect a GROUND to the motor case/frame then you have a defective motor. A pool motor is REQUIRED to be grounded. Mounted on a wood base your motor is not grounded and presents a hazard.
A GFI device (breaker or receptacle) compares the current going out on the hot wire with the current coming back on the neutral. If those two currents are different by more than the prescribed amount there is a problem and the GFI device trips. You want a working ground on equipment so the current to ground that trips the GFI is through the ground, not through you.
A GFI device (breaker or receptacle) compares the current going out on the hot wire with the current coming back on the neutral. If those two currents are different by more than the prescribed amount there is a problem and the GFI device trips. You want a working ground on equipment so the current to ground that trips the GFI is through the ground, not through you.