Based on the great feedback from all of you, I’ve redrawn and attached the revised concrete plan for the 54’ foundation west Wall. I’ve also hired TWO structural engineers, but they have given me different designs (essentially the two I originally posted, with rebar on the inside vs outside edge of the Wall). So I’ve decided to tap TBN expertise to help sort it out.
I’ll synthesize what I’ve concluded so far and hopefully can get additional feedback so I can finalize the design and move the project forward. To keep this post focused, I’ll address only the structural issues for this long Wall (and save discussion of drainage, pouring technique, concrete mix, conduit pipes, etc. for a later post). Basically I am combining both systems suggested, with an emphasis on one.
WALL IS SUPPORTED AT TOP AND BOTTOM
The Wall is indeed supported at the top and bottom, so “simple beam” analysis would indicate that the inside of the wall would be in tension and so rebar should go on the inside (I’m not a structural engineer, but picking up the jargon thanks to my friends here). The inside rebar system is essentially #5 rebar cage 18” on center.
BOTTOM SUPPORT -- GOOD
The support at the bottom is provided by both the 2x4 keyway and the rebar hooks placed in the footing and extending at least 30” up into the Wall. This should be sufficient to bond to the Wall and anchor its bottom. Eventually the slab will be added which will further anchor the bottom, but not until well after its backfilled.
TOP SUPPORT -- GOOD AT BOTH ENDS
The support at the Wall top is provided by the floor system, which is14” TJI joists with tongue and groove 3/4” plywood subfloor. This system should provide excellent support at either end of the Wall, where the 30’ end foundation walls are perpendicular to this Wall and serve effectively as pilasters. This floor system is anchored to these end foundation walls so that the floor provides that lateral support as well.
TOP SUPPORT -- POSSIBLY WEAKER IN CENTER
In the center of the 54’ Wall, the floor system is 27’ away from the end walls. It seems that this might be a point of weakness in the support of the Wall top, especially since the opposite wall is wood framed for garage doors and not backfilled. Forces from the sandy backfill might not be that strong to cause the floor to be pushed back, but then again it might be good to provide some insurance for that. The cost of the insurance rebar will be less than 5% of the total wall cost, so that seem like it would be worth it.
With top support weaker in the middle of its length, the Wall at its middle might behave like a “cantilevered beam” with the outside in tension. So I’ve added vertical rebar on the outside as well to counter a possible force that would want to push the wall in from the top if the floor system doesn’t resist it fully. The vertical rebar is #7 and is wired to the rebar hook coming up from the footing. Horizontal #5 rebar placed just to the inside of the #7 vertical bar provides additional support.
FOOTING
The footing was originally 12’ x 24”, considered sufficient for the soil conditions, was elongated by 12” to 36” wide to provide additional support for any moment forces that might arise at the middle of the wall. The depth was not altered since the soil support was adequate. A piece of horizontal rebar runs across the width of the footing to provide additional support.
OPEN QUESTIONS
Do you think this is a good enough design? Would it be improved if we were to tie the inside and outside rebars together somehow? Does the grade of rebar matter and if so what grade should I specify? Any other structural suggestions? Many thanks again!