The company I worked for had a project for the Army COE on which there were drawings AND specifications that both had to be met. Although the drawings indicated wire sizes that appeared to be "normal" for the circuit ratings, there was a spec that called for a certain maximum allowed voltage drop, and that the wire sizes may need to be adjusted. Due to distances, there were many 20A circuits that had to be wired with #8. One of the guys who worked on the project claimed there were a few circuits that needed #6. They physically tested the circuits with something like this:
circuit-analyzer.com