Electric service to barn

   / Electric service to barn #62  
I never heard of a farm meter but thats a good way to do it. I can see where the ground wire would not be required. It's sort of like another house on the transformer with it's own main panel. I think distance is the key. The second panel wants to be so far away that neutrals and grounds will never be in contact from one main to the other. But I have never seen that distance defined. What ever the inspector wants.
 
   / Electric service to barn #63  
I knew if I kept this up I would have to dig it out. NEC
Start with section 250-21a General comment to avoid current flow over grounding or grounded paths.
250-23 a explains that the premises service grounding electrode and the gounded service (neutral ) are tied together . It goes on to say that this connection shall not be made anywhere on the load side of the service disconnecting means. If you run a branch circuit out to the barn from this panel this means you cannot tie the nuetral to the ground anyplace else. That's why the screw that ties the neutral buss to the box it sits in is shipped loose. If its a main panel it goes in, if its a sub panel ,even in a barn it stays out. It is also the reason boxes have tapped holes to allow installation of separate groundbuss'.
There are many other sections that say ,in different ways that you must have grounding electrodes( long bars)
250-53 b could e confusing except that the box in the barn is NOT a service disconnect. I think this is the key. The Farm meter pan with two sets of lugs make the box in the barn a service and then the neutral buss is grounded there.
 
   / Electric service to barn #64  
6sunset6 said:
I knew if I kept this up I would have to dig it out. NEC

Since you had to dig it out, now go read 250.32(b). If you run a grounding conductor, you isolate the two. If you elect not to, and there are no other metallic paths, you can bond the two together at the barn.
 
   / Electric service to barn #65  
I don't have a b but I have an older version of NEC.. It's pretty minor but I have been in the electrical gounding business a long time and I like to have safe in my mind instead of whether or not to run an extra wire. Personal preferance .
 
   / Electric service to barn #66  
6sunset6 said:
I don't have a b but I have an older version of NEC.. It's pretty minor but I have been in the electrical gounding business a long time and I like to have safe in my mind instead of whether or not to run an extra wire. Personal preferance .

I understand, no prob. I've been in the electrical trade for many years myself, including enforcement of the NEC® for the last 18 years.
I think it was brought into the NEC® in 2002.
 
   / Electric service to barn #67  
Fishpick,
They finally put in our electric and water. Where the two ran in the same place they put them both in the same trench with the water below frost and the electric at about 24". I was watching to see if he was going to drop his bobcat in the trench when patially filling it before putting the electric in. Then he told me he almost put the minitrackhoe in the ditch. He went to turn to get off the ditch and it nearly fell in. He had to fill the ditch back in, drive the hoe off and dig it back out from the side. He said that wasted him about an hour. I was more upset that I missed the show :). I ended up with 4 strands of #2 Al direct bury wire and two empty 1" PVC conduit. He will then sink the grounding rods and I will attach the ground leads and have it inspected before I drive them home. The reason for the 2 PVC was that he was supposed to put in 2" conduit and run the service line through that. Then I would have had extra space to run a light switch back to the house if I wanted to. Then have a spare conduit for the telephone. Since he wnet direct bury on the cable I made him put in two small conduits. They are all laying next to each other so I bet I am going to have some noise in the phone. I tried the cordless phones in intercom mode and I could not hear my wife in teh barn but she could heare me with no problems. We will see what works.

Eric
 
   / Electric service to barn
  • Thread Starter
#68  
Eric_Phillips,
Cool! Sounds like the phone works just fine ;)
Tonight I'm planning on starting to do a bit of the electric project... got most of the pool grading done last night - so I'm on Honey-Do work release for the evening! Hope to pull the cable through the existing conduit back to the barn with a new LB and a expansion joint... that will get about 40' of the 130' job done :)

Maybe tonight we will even get the conduit in the garage set and up into the attic... which would be awesome!

I'll post progress and pics in the morning.

As for the discussion on the NEC - there are the 2 approaches in the 2 sections discussed - one is 3 wire - one is a 4 wire approach. I have never been a fan of having to float the neutral bus - that's why I chose the 3 wire route after talking with the inspector... for what I'm doing - and the type of expected draw - he actually was the one to "push" the 3 wire solution.
 
   / Electric service to barn #69  
I will be interested what the inspector says about my 4 wire system since we are using the same inspector. I assume you are not having any other metallic connections back to teh house? Since I think I will need to run a phone line I need the 4th wire.

Eric
 
   / Electric service to barn
  • Thread Starter
#70  
Last night got the project started - which ended up - through the evolutions of this posting to be different than expected.
I had (as Eric_Phillips stated) decided to have only the power out to the barn - no other cables - anything else I would want will be "wireless"... SO I decided to use the existing 2" conduit... as we started to pull out the existing wires (CAT5, coax, and a horry story of a single Romex run... we noticed that there was water in the conduit - and by water I mean A LOT...
Now - this was to be expected, in retrospect - since when the conduit was attached to the garage there was no expansion joint - and the LB snapped off - on the side of the house that gets all the rain...
So - hooked the air compressor up and blew out all the water we could...
Then - to get rid of the rest that wouldn't blow out - we put rags on a rope - about 3' apart and ran 4 of them through the conduit... first batch did a great job - second batch came out clean! We decided it was a cross between a colonoscopy and cleaning a gun!
Anyhow - got the #2 out into the barn through the conduit - up the inside of the garage wall between studs in conduit... a hairy turn in the attic made and a 10' section in the attic run...
Tomorrow night we finish the attic for sure, run down the garage wall and break into the basement... anything more than that is gravy...

I could post pictures of gray tubing... but I know this group - you all can close your eyes and imagine it...
 

Tractor & Equipment Auctions

Nissan 5k Forklift (A51039)
Nissan 5k Forklift...
2020 CATERPILLAR 326 EXCAVATOR (A51242)
2020 CATERPILLAR...
2013 Ford Explorer SUV (A50324)
2013 Ford Explorer...
2012 John Deere 7230R (A51039)
2012 John Deere...
https://www.accessnewswire.com/newsroom/en/healthcare-and-pharmaceutical/nerve-alive-supplement-reviews-inspired-by-nervecalm-for-natural-nerv-1044754
https://www.accessn...
2014 RAM 5500 FLATBED TRUCK (A51222)
2014 RAM 5500...
 
Top