Took the advice and met with my elec coop about relocating the pole near the middle between cabin and barn.
Below is a recap with answers from electric coop, sound about right?
Planning on running the existing 200amp svc to house (~150' up hill) and to barn/RV plugs which is about 270' away.
Questions:
1. Will this configuration allow 200amp svc to house and barn simultaneously?
Yes
2. Can I also run from pole directly to water well?
Yes, to a breaker for water well. Breaker can be under the disconnect on our pole or if you build a well house I would put the breaker in the well house.
3. Is this the right kind of wire? Not clear what URD means.
http://m.homedepot.com/p/Southwire-...eetbriar-Wire-By-the-Foot-55418499/205001902/
Yes, the URD is Underground.
4. What size conduit should I get?
Will fit in 2" but 3" is easier to pull through.
5. Will 4/0 4/0 2/0 be sufficient for the Barn at ~270'?
Yes, you will have voltage drop at 270' but you are sending 200 amps per leg from meter to barn. If you balance your load you will have plenty of voltage for barn and a couple RVs
Thanks for all your help!