I thought about doubling up on the cable run.
Just buy a 1000 ft roll of 10-2 with ground.
Run 500 feet and use all 3 wires for one hot side,
and run the same for the other hot side.
Drive a ground rod at the pump site and bond on to it.
The calculations seem to bear it out.
# 6 AWG wire has a diameter of .162
Which gives a cross sectional area of .0206
# 10 AWG wire has a diameter of .1019
Which gives a cross sectional area of .0082
So using all 3 wires in 10-2 w/grnd romex,
I get a total cross sectional area of .02445
Which is close to being a #5 AWG size, .02957 CSA
AWG size tables. http://www.powerstream.com/Wire_Size.htm
Don't think the NEC would allow this.
But I'm not subject to inspection.
Not to worry. A 1000 foot roll of 10-2 is out of my price range.
Pooh Bear
Just buy a 1000 ft roll of 10-2 with ground.
Run 500 feet and use all 3 wires for one hot side,
and run the same for the other hot side.
Drive a ground rod at the pump site and bond on to it.
The calculations seem to bear it out.
# 6 AWG wire has a diameter of .162
Which gives a cross sectional area of .0206
# 10 AWG wire has a diameter of .1019
Which gives a cross sectional area of .0082
So using all 3 wires in 10-2 w/grnd romex,
I get a total cross sectional area of .02445
Which is close to being a #5 AWG size, .02957 CSA
AWG size tables. http://www.powerstream.com/Wire_Size.htm
Don't think the NEC would allow this.
But I'm not subject to inspection.
Not to worry. A 1000 foot roll of 10-2 is out of my price range.
Pooh Bear