   / Electrical Questions... Lots of them! #11  
I don't think copper and aluminum have the same current carrying characteristics. Usually have to upsize for aluminum.

Let me start by saying I am NOT an electrician so I may be wrong BUT

I do believe you are correct and grsthegreat is wrong here.

When I built by barn, I used what the local COOP uses for their 100 Amp service, which is 1/0 underground. Which has 1/0 AL wire for the conductors and #2 AL forthe neutral. My choices were either this 1/0, 1/0, #2 Aluminum wire OR 2/2/4 copper wire. obviously the copper was ore expensive.

For 200A installs with aluminum wire they use 4/0 with 2/0 for the Neutral.

#2 aluminum xhhw is only rated @ 90A. I personally would not want to use that for 100A service. #2 copper would be okay though.

Again, I am no electrician, but I can read a chart Ampacity Charts
 
   / Electrical Questions... Lots of them! #13  
Let me start by saying I am NOT an electrician so I may be wrong BUT

I do believe you are correct and grsthegreat is wrong here.

When I built by barn, I used what the local COOP uses for their 100 Amp service, which is 1/0 underground. Which has 1/0 AL wire for the conductors and #2 AL forthe neutral. My choices were either this 1/0, 1/0, #2 Aluminum wire OR 2/2/4 copper wire. obviously the copper was ore expensive.

For 200A installs with aluminum wire they use 4/0 with 2/0 for the Neutral.

#2 aluminum xhhw is only rated @ 90A. I personally would not want to use that for 100A service. #2 copper would be okay though.

Again, I am no electrician, but I can read a chart Ampacity Charts

nope...not wrong....do it every day and totally legal. IF ITS UNDERGROUND. remember services require different rated levels than branch circuits. #2 copper is actually rated at 125 amps, and #2 alum is rated 100 amp for service use. as long as its underground.
its very confusing. these are the absolute minimums for the 50 foot run. personally i would use a 2/0 alum if it was my place just cause im always doing stuff overdone. but thats just me. and anyways it may be a mute point cause i still think that you wont be allowed to take anymore than 50 amps off of that existing panel legally. we usually upgrade the main service to 400 amps to run a dedicated shop circuit, then run 4/0 alum feeders to a 200 amp shop panel.
 

Tractor & Equipment Auctions

2011 Ford F-350 Knapheide Service Truck (A54814)
2011 Ford F-350...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2014 Dodge 5500 4X4 Bucket Truck (A55218)
2014 Dodge 5500...
2002 FREIGHTLINER FL70 DUMP TRUCK (A51406)
2002 FREIGHTLINER...
2015 KUBOTA 1140CPX RTV (A51406)
2015 KUBOTA...
2019 CATERPILLAR 745 OFF ROAD DUMP TRUCK (A52705)
2019 CATERPILLAR...
 
Top