Electrical Questions... Lots of them!

   / Electrical Questions... Lots of them! #11  
I don't think copper and aluminum have the same current carrying characteristics. Usually have to upsize for aluminum.

Let me start by saying I am NOT an electrician so I may be wrong BUT

I do believe you are correct and grsthegreat is wrong here.

When I built by barn, I used what the local COOP uses for their 100 Amp service, which is 1/0 underground. Which has 1/0 AL wire for the conductors and #2 AL forthe neutral. My choices were either this 1/0, 1/0, #2 Aluminum wire OR 2/2/4 copper wire. obviously the copper was ore expensive.

For 200A installs with aluminum wire they use 4/0 with 2/0 for the Neutral.

#2 aluminum xhhw is only rated @ 90A. I personally would not want to use that for 100A service. #2 copper would be okay though.

Again, I am no electrician, but I can read a chart Ampacity Charts
 
   / Electrical Questions... Lots of them! #13  
Let me start by saying I am NOT an electrician so I may be wrong BUT

I do believe you are correct and grsthegreat is wrong here.

When I built by barn, I used what the local COOP uses for their 100 Amp service, which is 1/0 underground. Which has 1/0 AL wire for the conductors and #2 AL forthe neutral. My choices were either this 1/0, 1/0, #2 Aluminum wire OR 2/2/4 copper wire. obviously the copper was ore expensive.

For 200A installs with aluminum wire they use 4/0 with 2/0 for the Neutral.

#2 aluminum xhhw is only rated @ 90A. I personally would not want to use that for 100A service. #2 copper would be okay though.

Again, I am no electrician, but I can read a chart Ampacity Charts

nope...not wrong....do it every day and totally legal. IF ITS UNDERGROUND. remember services require different rated levels than branch circuits. #2 copper is actually rated at 125 amps, and #2 alum is rated 100 amp for service use. as long as its underground.
its very confusing. these are the absolute minimums for the 50 foot run. personally i would use a 2/0 alum if it was my place just cause im always doing stuff overdone. but thats just me. and anyways it may be a mute point cause i still think that you wont be allowed to take anymore than 50 amps off of that existing panel legally. we usually upgrade the main service to 400 amps to run a dedicated shop circuit, then run 4/0 alum feeders to a 200 amp shop panel.
 

Tractor & Equipment Auctions

2014 Lamar Pipe Trailer (A60460)
2014 Lamar Pipe...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
KBH Tender Trailer (A56436)
KBH Tender Trailer...
2018 INTERNATIONAL LT625 TANDEM AXLE SLEEPER (A59575)
2018 INTERNATIONAL...
2004 MACK CV713 MIXER TRUCK (A55745)
2004 MACK CV713...
2021 KOMATSU WA200-8 WHEEL LOADER (A60429)
2021 KOMATSU...
 
Top