There is no problem using a HEAVIER wire, as long as there is a 15 amp breaker protecting the 15 amp receptacle. I had a kitchen wired last year and we ran some 12 gauge to 15 amp receptacles on 15 amp breakers because we got a great deal on the wire.

Agree with that. I should have clarified and said 12 gauge wire with appropriate 20 amp breaker using 15 amp outlets.

In your case, if I scored a deal on 12 gauge wire, I would have installed 20 amp breakers (same cost as 15 amp ones) and 20 amp receptacles (minimum increase over 15 amp) and enjoyed the benefits of a stronger circuit. In fact, it is a code requirement to wire kitchens on 20 circuits in my county as well as bathrooms.
 
   / Electricians: Range wiring and breaker sizing code #32  
Sorry LD1 I could have picked a better time of day to answer your questions. And maybe a better explanation.
With your breakers you are protecting the circuit at it's allowable ampacity. So if you have a 15A circuit, you need all the components to complete that circuit. You need a 15A breaker, wire rated at least 15A and a 15A receptacle. If you need a 50A receptacle, you need a 50A breaker, 50A wire minimum and a 50A receptacle. So you're actually protecting the circuit. You can't plug a 50A range into a 60A circuit because the circuit is not protected properly with with the 60A breaker. You don't have a 60A rated receptacle. Table 210.24 of the 2014 NEC lists the circuit sizes and their protection.
With your cell phone charger, yes you've plugged it into a 15A circuit/receptacle protected by a 15A breaker. The circuit is protected properly.


But now let me say this, I don't have people do things because I "want" them to. I do it according to the code. I hear this every day, "I did it the way you wanted it". It has nothing to do with what I want. If I can't show you in black and white, then you don't have to do it. Actually one of my inspectors no longer has a certification to inspect because he kept tossing his "personal opinion" in at his inspections.


And that is a professional posting, thank you Inspector507!

Folks forget that the NEC, Building Codes and other regs are designed to protect their very lives and inspectors exist to interpret and apply the codes.
 
   / Electricians: Range wiring and breaker sizing code #33  
If the original electrician installed the breaker he was wrong. The outlet for the range is the reason the breaker is to be no larger than 50 amp.
If the breaker went bad and the previous owner went to a hardware store and purchased the wrong breaker it still does not make it right. The NEC states the breaker is there to protect the circuit. The circuit at the time of wiring inspection had a 50 amp recectacle. If this was originally a wall mount range/double oven the breaker could be 60 amp because the range could have been rated by the manufacturer at 60 amp.
 
   / Electricians: Range wiring and breaker sizing code #34  
I'm not an inspector nor an electrician, but my take on it is that the stove is a dedicated circuit. Ie the only thing plugged into it is the stove. In my house when we moved in 10 years it was new and I was surprised to see just how many dedicated circuits there were. One for the stove, dryer, AC, water heater, refrigerator, MICROWAVE, GARAGE DOOR OPENER.

I guess my point is they are heave amp draw items so that is why the dedicated circuit. General use items are not heavy draw. That is why a 15 or 20 circuit is standard? Most other thing plugged in do not require heave amperage.

Heck sorry I forgot where I was going with that.

Sent from my iPhone using TractorByNet
 
   / Electricians: Range wiring and breaker sizing code #35  
Maybe the breaker has to be sized for the lowest amp rated link in the chain. Ie 15 amp outlet 20 amp wire= need for 15 amp breaker.

Sent from my iPhone using TractorByNet
 
   / Electricians: Range wiring and breaker sizing code #36  
Maybe the breaker has to be sized for the lowest amp rated link in the chain. Ie 15 amp outlet 20 amp wire= need for 15 amp breaker.

Sent from my iPhone using TractorByNet

If only one outlet on a 20 amp breaker it must be a 20 amp outlet. If two or more 15 amp outlets they can be on a 15 amp or a 20 amp breaker.
 
   / Electricians: Range wiring and breaker sizing code #37  
Okay, I'll buy that. I am not in compliance with the NEC via not being in compliance with the MFG directions.

But since the house was built in 1995, and I am either the second or third owner, I doubt this range is original.

Not that it matters at this point, again, this is just information seeking as I am going to change the breaker, but......

As an electrician, when wiring a residential house, how do you know what size range they will be using? or that it wont be different in the future? Same goes for dryer and waterheater? Allthough I think 30A feeding them is pretty standard.

I know that this isnt the only time I have seen 60A breakers for a range. Probably 50% of the houses I looked at are 60A ranges, the rest are 50A


I totally get your analogy regarding a tiny fragile device being allowed to plug into a 15, or 20 amp receptacle. For sure, the breaker can not be relied upon to prevent the appliance from melting or burning.

In your stove case, what they are saying, is that the house's stove receptacle is not rated for the 60 amps that the wiring and breaker are. In other words the breaker, wiring and recepticle have to all be rated.
 
   / Electricians: Range wiring and breaker sizing code #38  
Maybe the original range was a 60 amp hardwired.

Then somewhere along the line the range was replaced with a 50 amp model with a 50 amp cord needing a 50 amp receptacle and the circuit breaker was left unchanged.
 
   / Electricians: Range wiring and breaker sizing code #39  
Maybe the original range was a 60 amp hardwired.

Then somewhere along the line the range was replaced with a 50 amp model with a 50 amp cord needing a 50 amp receptacle and the circuit breaker was left unchanged.
Very well could have been but now there is a 50amp receptacle in the picture which is why it can't have a 60amp breaker!
 
   / Electricians: Range wiring and breaker sizing code #40  
Run into these things all the time...

Sometimes it was just wrong from day one and not caught... more often than not, it was altered at sometime creating the problem.

One of the homes I was selling had a lifetime Hoyt all copper water heater circa 1955 as was the house... the inspector did a lengthy write up on TPR valve and seismic bracing and typically he would be 100% correct to call this out as a code violation 40 years later because just how many homes still have the original 40 year old heater?

Some of the old Berkeley California homes dating from the 20's still have the Humphrey continuous hot water heaters... basically a copper coil with a flame and no storage tank... none of these have TPR valves.

A common electrical defect is not grounded 3 prong outlets when no ground exists... so long a only 2-prong outlets are used... no problem... again, the issue is improper alteration.

Another is lack of safety glass in shower doors, tub enclosures, doors and windows within so many inches of the floor.

It's totally up to you how you respond... ranges are one of those areas where the appliance was traditionally hardwired to a dedicated circuit... even in homes through the 1960's... it was also cheaper to hard wire.

A lamp is not considered stationary... a major appliance is.

My last Home Inspector checked the AC circuit carefully... the cable and breaker is rated at 50 amps and goes to a 30 amp fused disconnect within 4' of the compressor which is fine... the builder had sized the circuit for a larger unit...
 

Tractor & Equipment Auctions

2016 Big Tex 24ft. T/A Flatbed Trailer (A50323)
2016 Big Tex 24ft...
2011 VOLVO VNL670 SLEEPER (A51219)
2011 VOLVO VNL670...
UNUSED CFG Industrial H15R Mini Excavator (A47384)
UNUSED CFG...
2020 KUBOTA RTV X1100C UTV (A51406)
2020 KUBOTA RTV...
(INOP) NEW HOLLAND B95 BACKHOE (A50459)
(INOP) NEW HOLLAND...
Gehl 1870 Round Baler (A50514)
Gehl 1870 Round...
 
Top