The NEC gives a mulligan to 15 and 20 amp circuits. There's so many of them out there, for the most part they work OK, it would cost a fortune to require that every device plugged into an outlet be capable of 20 amps.
Think about it: the logical thing would be to say, yes, every device on the circuit has to be capable of handling the current of the circuit breaker. For a dedicated circuit that's not unreasonable. For general purpose circuits it would mean that everything would have to be 12ga wire, because 15 and 20 amps use the same outlets. More practical just to wave the magic wand and say that low-amperage circuits aren't a problem.
Yes, I think you hit the code logic hit on the head. For general use circuits, everything that gets plugged in is much lower draw and often has tiny wires. 18 ga is not code for any house wiring, but is fine for a lamp, for example. But when it is dedicated, then you must match as there is an assumption that the appliance needs the full rating, and so the whole circuit should be rated the same. Still not sure about plugging in a 50A stove on a 60A circuit, but I guess the code logic says that is not kosher... strange but true, I guess.