Electricians: Range wiring and breaker sizing code

   / Electricians: Range wiring and breaker sizing code #61  
We could try this another way. A male plug on a cord to plug into a 120v 15 amp receptacle has one configuration. A male plug to plug a cord into a 120v receptacle 20 amp receptacle has another configuration. A male plug to plug into a240v 40 amp receptacle has another configuration. A male plug to plug into a 240v 50 amp has another configuration.

Go to graingers.com and download the receptacle and plug chart, do a bing search and see that every ampacity and voltage has receptacle and plug. More if you consider twist lock which also has ratings to the configurations. receptacles.jpg
 
   / Electricians: Range wiring and breaker sizing code #62  
I'm not a licensed electrician or electrical engineer, just a mechanical engineer, but I successfully wired my new house myself and passed inspection with no findings.

It is my opinion (maybe some here more qualified can confirm) that the MAIN thing the NEC is concerned with, particularly for residential wiring, is protecting the HIDDEN wiring within the house that may overheat and cause a fire. This includes wiring ("cords") to large amp "fixed" appliances. It is not really concerned about your exposed lamp or cell phone charger cord.

And that HIDDEN wiring for large fixed appliances with a receptacle/cord like in this case includes the receptacle.

50 amp rated receptacles

https://www.google.com/search?q=50+...-Straight-Grounding%2Fdp%2FB004P3P2L0;500;500

are DIFFERENT than 60 amp rated receptacles

Google Image Result for

So the problem here WITH THE CIRCUIT is really that the receptacle is under-sized. The OP could probably rectify the inspector's concern by changing out the receptacle to a 60 amp. But then he'd have a circuit that the range wouldn't plug into. So the much better solution is to down-size the breaker to match the receptacle (which the range is already using).

JMHO -Jay
 
Last edited:
   / Electricians: Range wiring and breaker sizing code #63  
I'm not a licensed electrician or electrical engineer, just a mechanical engineer, but I successfully wired my new house myself and passed inspection with no findings.

It is my opinion (maybe some here more qualified can confirm) that the MAIN thing the NEC is concerned with, particularly for residential wiring, is protecting the HIDDEN wiring within the house that may overheat and cause a fire. This includes wiring ("cords") to large amp "fixed" appliances. It is not really concerned about your exposed lamp or cell phone charger cord.

And that HIDDEN wiring for large fixed appliances with a receptacle/cord like in this case includes the receptacle.

50 amp rated receptacles

https://www.google.com/search?q=50+...-Straight-Grounding%2Fdp%2FB004P3P2L0;500;500

are DIFFERENT than 60 amp rated receptacles

Google Image Result for

So the problem here WITH THE CIRCUIT is really that the receptacle is under-sized. The OP could probably rectify the inspector's concern by changing out the receptacle to a 60 amp. But then he'd have a circuit that the range would plug into. So the much better solution is to down-size the breaker to match the receptacle (which the range is already using).

JMHO -Jay

NO. Sorry but I disagree. The breaker's sole purpose is to protect the wire from the breaker to whatever is connected to the circuit. The breaker can't have a higher rating than anything downstream, wire, receptacle, etc. It can have the same rating as the wire and receptacle, and in this case the appliance. Since the range can take 40 or 50 amp circuit 40 is OK and 50 amp is maximum any wiring, breaker, or receptacle is allowed for this dedicated circuit. Essentially the breaker has to cover the lowest, while not exceeding the highest allowable amp draw for the appliance.
 
   / Electricians: Range wiring and breaker sizing code #64  
You could direct wire the range and be done with it
 
   / Electricians: Range wiring and breaker sizing code #65  
NO. Sorry but I disagree. The breaker's sole purpose is to protect the wire from the breaker to whatever is connected to the circuit. The breaker can't have a higher rating than anything downstream, wire, receptacle, etc. It can have the same rating as the wire and receptacle, and in this case the appliance. Since the range can take 40 or 50 amp circuit 40 is OK and 50 amp is maximum any wiring, breaker, or receptacle is allowed for this dedicated circuit. Essentially the breaker has to cover the lowest, while not exceeding the highest allowable amp draw for the appliance.

Do you mean this for any circuit or only "dedicated" circuits?
The breaker can't have a higher rating than anything downstream, wire, receptacle, etc.
 
   / Electricians: Range wiring and breaker sizing code #66  
NO. Sorry but I disagree. The breaker's sole purpose is to protect the wire from the breaker to whatever is connected to the circuit. The breaker can't have a higher rating than anything downstream, wire, receptacle, etc. It can have the same rating as the wire and receptacle, and in this case the appliance. Since the range can take 40 or 50 amp circuit 40 is OK and 50 amp is maximum any wiring, breaker, or receptacle is allowed for this dedicated circuit. Essentially the breaker has to cover the lowest, while not exceeding the highest allowable amp draw for the appliance.

You're kinda saying the same thing I am except for the highlighted part and maybe you missed where I said that "And that HIDDEN wiring for large fixed appliances with a receptacle/cord like in this case includes the receptacle.".

Lemme ask you this: you have a dedicated circuit for your refrigerator. Say your refrigerator max amperage is 8.5a. So you have an 8.5a breaker on that?

- Jay
 
   / Electricians: Range wiring and breaker sizing code #67  
The inspector is correct the breaker size is to be the same size or smaller than the device being served,,

WRONG.
 
   / Electricians: Range wiring and breaker sizing code
  • Thread Starter
#68  
Certainly some confusion...
 
   / Electricians: Range wiring and breaker sizing code #69  
Never smaller
 
   / Electricians: Range wiring and breaker sizing code #70  
See what you started LD?:laughing::D
 

Tractor & Equipment Auctions

2007 Amkus Rescue System (A50322)
2007 Amkus Rescue...
UNUSED CFG Industrial QK18R Mini Excavator (A47384)
UNUSED CFG...
2015 Dodge 5500 4X4 Bucket Truck (A52128)
2015 Dodge 5500...
2014 Gillig G27B102N4 31+56 Low Floor Passenger Bus (A50323)
2014 Gillig...
Crosley 10ft. Hydraulic T/A Dump Trailer (A50322)
Crosley 10ft...
BUSH WACKER ST-180 ELITE BATWING ROTARY MOWER (A51406)
BUSH WACKER ST-180...
 
Top