I'd drop by the local FD and chat with them before putting anything in. They can give you more options on pumps, and specifically tell you what they need for a FDC.
You might look at a gas pump. It will work without power. Also, most times it is best to cut power to where you are fighting fire, lest you risk getting shocked.
Wildland flow is in the rnage og 35-60gpm, depending on the nozzle setting. Use only the water you need, but use enough to put the fire out; you don't want it to flare behind you. Most Engines only have 500-750 gallon tnaks, so water conservation is an issue. A wildland nozzle still likes to have 100psi, even at lower flows. Since it is a spray nozzle, it needs to work around 100psi or else it will not form a stream properly. Remember too, friction loss. A few lengths of single jacket wildland hose will drop pressure quickly.
Friction loss is FL=CQ2L
C for 1-1/2" hose is 24
Q=gpm/100
L=hose length/100
200' of 1-1/2" hose running a max of 60gpm for a wildland nozzle would be
FL=(24)(60/100)2(200/100)
FL=(24)(0.6)2(2)
FL=17.28
So, you need 117psi at the pump to properly flow 60gpm at 100psi to a wildland nozzle with 200' of 1-1/2" hose. For 400' of hose, bump it up to 134psi.
A structure attack flows more water, 100-150gpm. 1-3/4 and 2.5" lines/nozzles can flow a LOT of water. I would guess that you would not use more than a wildland attack setup, as the nozzles and hose are EXPENSIVE.
If you want to figure it out though, here's the values:
C=15.5 for 1-3/4" line
C=2 for 2.5" line
You need to find out what equipment you will want for your hoselay, so you know the PSI and gpm requirements. That will give you a better idea of the pumping capability you will need.
The station I used to work at used gas powered pumps, and just moved from floating pumps for use in lakes, streams ect, to a gas pump with a short suction line.