That is how I look at it too. I don't see the need to run a 20kw genset for power outages, I get by with alot less.
A typical set of heat strips in an electric furnace will need 19.8kw, a standard electric water heater (40 gallon) is 4.5kw, add a few smaller appliances and lights to this and you are past 30kw. Removing the two heating loads of 24.3kw can make a huge difference in what is needed. The amount of fuel needed could be conserved too, lessening the chance of running out in the middle of a long power outage.
i guess it all depends on the surge allowance of the generator. my 4.5 ton heat pump pulls 120 amps at startup...mind you only for a second or 2, but it does. Also depends on amount and size of the supplemental heat strips. ive wired up 20KW heat strips on units here in Idaho.