grsthegreat
Super Star Member
most propane systems have a primary regulator (10#) at tank. then a small line (1/2" usually but ive seen 3/4" for real long runs) to house regulator. after the house regulator the pipe sizes always increase...depending on load. my house uses 1-1/4" pipe after regulator.I have 1/2" from the 500 gallon tank. There is a regulator right behind where the genset will sit. That one goes into the house for the furnace and stove. I plan on having another regulator installed in the main line for the genset only. I'm looking at the 13K, but may still go smaller.
On my own generator, I tee'd off underground and caught the 1/2" poly pipe. ran that to generator. then installed a secondary regulator at generator.
it all depends on size of generator used. a 13kw unit can burn 225,000 BTU of fuel at max. a 22KW unit can burn up to 355,000 BTU at max. secondary regulator has to be sized accordingly.
PLEASE NOTE. generator will need to be 5 feet from any window or door opening, and 3 feet from the back from any exterior wall. also 5' from ANY fuel regulator. the owners manual that you can see online have a good drawing.