First of all, thanks for all the feedback. For me the opportunity to bounce an idea around is just as valuable as the right answer in the first place.

Attached photos show my situation. Just to clarify, I don't wish to disconnect the generator feed- I might need it. Also, I subconsciously have wondered about the risk of feeding juice back into the grid. The 4 square box to the right of the gen panel appears to be only a receptacle, not a switch. The instructions to the right imply that the transfer must be done manually--?? by switching off the feed from the main, and switching on the feed from the gen ??

In tracing wires between the panels and from the main panel out into the house, it appears that the electrician and/or homeowner just chose which circuits to include and which to leave out.

What I think I really want is an automatic transfer from the generator to the main panel w/o having any individual circuits connected between the two. If this is not possible I won't fight it, but I would like know why.
 

Attachments

  • IMG_1621.JPG
    IMG_1621.JPG
    2.9 MB · Views: 510
  • IMG_1622.JPG
    IMG_1622.JPG
    2.6 MB · Views: 463
  • IMG_1623.JPG
    IMG_1623.JPG
    2.3 MB · Views: 176
   / Generator wiring #12  
What I think I really want is an automatic transfer from the generator to the main panel w/o having any individual circuits connected between the two. If this is not possible I won't fight it, but I would like know why.

That type of isolated automatic system is not possible. How would the generator know when to turn itself on and make an automatic transfer if it was not able to constantly sensing the incoming power to be able to tell when it failed? And to do that it has to be connected to the main panel.

If you want completely isolated circuits what you want is a less expensive and less complicated manual transfer switch wired between the the incoming lines to your house and the main panel. Installing that will require an electrician and also an inspection. Then you can positively disconnect the main when it connects the generator.

What you have now looks like somebody's homebrew & dangerous system that can backfeed the grid. You could be liable if that happens. I'd either put in a transfer switch or isolate it completely.
I know that's not what you want to hear, but better that you know.
 
Last edited:
   / Generator wiring #14  
THink you need to call electrician (one who specializes in generators/transfer switches) and have them come take a look and explain to you what you have... And may any changes you require if you want to make system operate differently...

I went totally simple, manual transfer switch for well only (240V) because is you have water everything else is easy.... Just run 12 gauge extension cord from generator to fridge and computers and go into "camping mode".... Survived 8 days this way due to power outage from wildfire while local utilities work almost non stop to restore power...

After seeing the profusion of wire nuts in main panel, I don't think I would venture in there....

img_1621-jpg.771875





What I see here is a series of breakers that one set needs to be turned off, and another turned on to transfer power... WITH NO SAFETY INTERLOCK.... Call electrician....

img_1622-jpg.771876
 
Last edited:
   / Generator wiring #15  
First of all, thanks for all the feedback. For me the opportunity to bounce an idea around is just as valuable as the right answer in the first place.

Attached photos show my situation. Just to clarify, I don't wish to disconnect the generator feed- I might need it. Also, I subconsciously have wondered about the risk of feeding juice back into the grid. The 4 square box to the right of the gen panel appears to be only a receptacle, not a switch. The instructions to the right imply that the transfer must be done manually--?? by switching off the feed from the main, and switching on the feed from the gen ??

In tracing wires between the panels and from the main panel out into the house, it appears that the electrician and/or homeowner just chose which circuits to include and which to leave out.

What I think I really want is an automatic transfer from the generator to the main panel w/o having any individual circuits connected between the two. If this is not possible I won't fight it, but I would like know why.
The system that you currently have has just a few circuits on the generator power feed. Does the cover for the generator panel have an interlock device to prevent the 2 "main" breakers being on at the same time?
If it doesn't it does not meet code or general safety guidelines.

If you wish to have a whole house transfer switch in will need to be installed before your primary incoming panel.
It can be an auto or manual transfer switch. If auto it will sense the incoming voltage, and on fail start the generator then transfer from the utility to generator power.

If you wish to have a smaller standby generator to handle a few dedicated circuts you would need a panel similar to what you have now but with a built in manual transfer switch.
similar to this;
1669394026628.png


Your existing system could be upgraded with an inter lock so only the main or only the generator breaker could be on at any time.
similar to these,
Interlock Kit & Accessories For Your Home | Generator Interlock Kit

1669394313813.png
 
   / Generator wiring #16  
I have a (side load) generator panel that has 6 circuits that I power with a 7500 watt dual fuel portable generator .each breaker has 3 positions
Line -from JNEC
Off- Off to work on circuit
Gen- Power from generator

This is wired into main breaker box so that no power will ever back feed. It’s a manual system you have to plug in generator and throw the switches for the circuits you want to power but at the time it was the best method for us.
 

Attachments

  • image.jpg
    image.jpg
    2.3 MB · Views: 63
   / Generator wiring #17  
I fool with generators often. First one is an Allis Chalmers 50 kw at my shop. It does single and three phase with a brushless generator. Second one I just put a circuit board in because it wasn't coming on weekly for its self check, 175 kw. Then after I had it working, the power went off two days later. The pull on solenoid was not holding throttle open. It was 21 years old, so I had a dandy of a time finding one. Finally did, but it was different. Had to use the guts out of old one and magnet coil from new one to make it work. Had to fix it, farm owner was ready to pull the trigger on another lightly used one for 30 grand. Third one is fine. Welder needed a circuit board. I have another welder, a few years older, that needs an exciter or stuck brushes, have not investigated it yet. Runs fine but no weld, only sparks. Electricians call me to go on big farm generator calls, because they don't know much about them. So when you have 25,000 chickens that Tyson wants $23.00 each for, it becomes critical. Generator runs two houses. 12,500 birds in each house. If you get them automatic transfer switches, ants love them things. They won't work with ants around. Just had two houses die a few months ago, not me, a customer. Chickens dead in 30 minutes. Their houses are full tunnel and don't have the side curtains like the one pictured. Side curtains have an automatic drop in case of a no power situation. So, power went off, gen was not on, no fans moving air, all birds died. Generator did not come on. Turns out they were using fuel from generator tank to run the tractors. Plus the weekly self check uses fuel too. Generator tank was empty and I can't fix that problem. That is their responsibility as a farm owner to keep the tank full. Which, they had 6 houses, I just tore down three of theirs that collapsed in the 18" snow we had. I'm fine with them using fuel out of gen tank because it keeps fresh fuel in there. But, it has to be kept topped off.

I don't see a problem with the situation you have. Maybe look into understanding it instead of undoing it. Since generators became popular, power companies ground out the wires they are working on. That will toast your generator. Just turn utility main off on your side of meter. Crank generator and turn the breakers on that you need. When power comes back on, turn off generator breakers, turn on utility breakers. I see no problem with that. Seems a simple trouble free experience. Or, you can go automatic, and it gilflirts when you need it, and you wait on a "specialized technician" that can figure out all the load sensors. Then when it (technician) shows up, you done froze for a week and power is back on anyway. That 1979 stuff ain't so bad. I drove to Alaska and everywhere else I want to go in a 1976 pickup, recently. If I leave my driveway and turn south, 21 miles to Louisiana.
 

Attachments

  • IMG_20221110_171822.jpg
    IMG_20221110_171822.jpg
    2.4 MB · Views: 77
  • IMG_20220619_204636_1CS~2.jpg
    IMG_20220619_204636_1CS~2.jpg
    2.1 MB · Views: 68
  • IMG_20220619_204341.jpg
    IMG_20220619_204341.jpg
    2.1 MB · Views: 73
  • IMG_20220904_175942.jpg
    IMG_20220904_175942.jpg
    2.6 MB · Views: 74
   / Generator wiring
  • Thread Starter
#18  
More feedback = more valuable. Regarding an automatic transfer, I wasn't thinking of a generator that would come on automatically, but a device that would automatically switch the panels from incoming grid juice to gen juice when the generator is started up with a pull cord. This isn't the first time I have imagined devices that don't exist.

The concept of a manual transfer switch is most appealing. IMHO manual anything is almost always better than automatic. The comment that my system appears to backfeed the grid may be enough proof that it has never been used. The observation that the well pump is all that is truly necessary is spot on, but maybe add the refrig.
 
   / Generator wiring #19  
You can add a manual interlock to the system in pictures, and you can use it as is. Leaving it without the interlock is very dangerous. If someone turns on the 2 pole 20 breaker attached to the twistlock generator supply outlet, you have a death trap (Open, exposed terminals)



MUR100PUL-1200x897.jpg







there is no automatic transfer switch that works on manual start generator. Least, ive never seen one.
 
Last edited:
   / Generator wiring #20  
The few times I run our 9kW portable generator I simply go in this order:
1) Turn main and all breakers off in main panel box, (except to garage 250 ft.away.)
2) Connect generator to welder outlet, leaving just garage main and welder breaker on.
3) Run generator.
4) At house turn well pump and water heater breaker on, as well as refrigerator.
5) Meter display let's me know when power is restored. A pilot light on main breaker meter side does same thing.
6) Shut generator off.
7) Disconnect generator.
8) Garage breakers on.
9) Main breaker on and others in main box.
 
 