Geothermal heating/cooling question

   / Geothermal heating/cooling question #1  

Z-Michigan

Veteran Member
Joined
Jan 2, 2007
Messages
1,790
Location
Central-western UP Michigan
Tractor
Kioti DK5010HS
Wondering if anyone has expertise with geothermal systems to advise on an issue - not sure if it's a feature or a problem.

I have a 1600sf house built in 1999. It is very conventional wood frame 2x4 construction, two stories, nothing unusual. While originally set up with a propane furnace and, as far as I can tell, no AC, around 2002 the prior owner installed a closed-loop geothermal heating/cooling/hot water system. The propane furnace remains as a backup for cold days when the geo can't keep up. There is no separate AC, and the propane water heater is physically in place but not turned on; it serves as a holding tank before the geo water heater tank. We moved into the house last November so we don't have even a full 12 months here yet.

This is a closed-loop system with a ground loop buried (I am told) 8 feet below grade and running a couple hundred feet long. This system does not involve a well or a pond. We had the system inspected about three months ago and no repairs were suggested.

I have a basic understanding of how the geothermal system works, as being basically a fridge type condenser system that can work in either direction to transfer heat either from ground to house (winter) or from house to ground (summer). I am not an expert on the system by any means.

Here's the issue: it's a hot summer here in Michigan. We set our cooling at 70. Most days the house stays at 70; on hotter days if often gets up to 73-75 in the mid to late afternoon and then cools back down. However, there have been two days - today and July 4 - when we had friends over and we were both cooking inside and opening doors frequently because we were grilling outside. On both days, the house temperature got to be over 80, even with the thermostat set at 70. Between July 4 and today the system has been working fine, even on 95+ degree days.

Can anyone tell me if this is a normal feature of a geothermal cooling setup? It is a bit frustrating to have people over on a hot day and have the house heat up!

Related question 1: given this type of ground loop, I am wondering if the capacity to cool erodes by end of summer, due to too much heat being put into the ground surrounding the pipe. We are having an unusual drought in my area, with less than 1" of rain in the last 8 weeks when 5" or more would be normal; I'm also wondering if the drought is both causing the ground temperature to increase and reducing its heat capacity. Also the correlating question: does the heating capacity fade at end of winter as too much heat is taken out of that same area?

Related question 2: since this is also our supply of hot water, would I ever get a benefit on a hot day from running hot water from faucet to drain, presumably pulling heat out of the working fluid and allowing more cooling capacity? Or am I making a bad assumption about how things work?
 
   / Geothermal heating/cooling question #2  
No expert here but a few thoughts:

Likely your system is like any other heating/cooling system, it is rated at a certain output and if your load exceeds that rating it will not be able to keep up. This could be the size of your ground loop, the size of the heat pump unit, your blowers being unable to exchange enough air.

I would get some of those cheap little thermometers and stick them in a couple of vents. (or you could use just one and walk around). Watch the temperatures throughout the day and see if it varies much. If it is putting out 60 degree air in the morning and 70 degree air in the hot part of the day I would say your loop or pump can't keep up. If the temperature stays pretty much the same then you are probably not exchanging enough air.

If it does rise during the hot part of the day you can try draining out all your hot water and see if it comes back down some, this will tell you if that would help or not.


I am curious as to whether or not you think your power bill is 'cheaper' compared to a regular setup. I read somewhere the system pretty much runs constantly so I would think it uses a lot of power.

Charles
 
   / Geothermal heating/cooling question
  • Thread Starter
#3  
Thanks. As far as I can tell the system is significantly cheaper. My prior house was similar sized (1420sf ranch) and had natural gas heat/water and electric for everything else including AC. It was only 25 miles from here so identical climate. That house was built in 2003 and was very well insulated. I probably paid around $200/month average for gas and electric combined, with an occasional cold winter month pushing toward $300. With this house my electric bills run just over $100, half of which is power for the geothermal system - which is metered separately and costs only about half as much since it's treated as electricity for heat which for some reason gets a lower rate. We have a fairly large propane tank - I think it's 1000gal but it might be only 500 - and using propane for backup heat, all cooking, and clothes drying, our propane use is almost imperceptible. The prior owner told us they only had to fill the tank once ever 3 years and I think that's believable (and I realize most people with propane heat would use 3-5 tanks per year). In fact the propane company that supplied the prior owner's tank is mad at us because we haven't bought any more from them. They're a PITA to deal with so once this tank runs dry we're giving it back and having a different, friendlier company supply us a new, smaller tank.

The downside of geothermal is that the initial cost is something like $10-20k, serious money. Glad I didn't pay for it! But once it's installed, it seems to be very economical.
 
   / Geothermal heating/cooling question #4  
Well there are a lot of circumstances that could be coming into play. First who designed it and for what load. I'm no expert either but I have had mine for 9 years and I grill the tech every time they come out to check it. They work just like a heat pump, they work on recovery and maintaining. Insulation is a major issue in that respect. They have to respond and MAINTAIN the temperature! Insulation is a major issue in that respect. They DO NOT respond like a conventional system were they fire to set point and stop. Once a geo unit gets the house to temperature it continues to run to maintain temperature in a stage one loading. Do you turn the system off and on?? When it's comforatable do you turn to unit off? Again, a conventional system can be run by turning the system on and off. A geo unit can not be operated this way, it has to stay on and be in operation all the time because it does work on recovery and maintaining!!!

If it's loaded, it's probably running in stage 2 (or emergency in the case of heating). I would guess, if your system is not keeping up, it's insulation or undersized. You should see at least a 25 degree difference in house temperature and out put air. If it's 80F inside your output air should be at least 65F or less!! Another factor, in my case, is a multi-level system. I heat and cool a 3600 ft log home, 3 floors, each with a thermostat and automated dampers. In order for the house to maintain, the thermostats have to be somewhat synchronized. If I want to load the system to work more, each setting has to see a >2 degree difference in order to go into phase 2. If one is within that 2 degree range it will revert back to phase 1 and try to divert the air (with the dampers) to the levels that need the temperature. Could it be the unit is not going into stage 2???

My system tells me when something is wrong (etal.... low freon, low water flow etc...) with warning lights. Water flow is very important also in the system, check your level and for visable water pockets (air bubbles)! For what it's worth, flow should be >10gpm in phase 2. This summer has been a hot one, house is comfortable all the time and I'm averaging about $140 a month, winter is about $80. Keep us up to date, I'd like to know more about whats happening to your system. I may learn something that I need to know about mine! Good Luck!
 
   / Geothermal heating/cooling question #5  
I have a Water Furnace 3 ton closed loop system for my 1500 square foot 1.5 story house (r30 in ceiling and r19 in the walls). The units are sized for ideal application and for doors that are closed most of the time. From what I understand, the units which are sized just right will be better at dehumidifying than a system that is too large for your home.

I would guess that the cooking and frequent open doors just temporarily over burdened your system.

Once, on a hot 95+ degree day while we had company and my wife was cooking with most of the burners on the stove, our unit couldn't quite keep up. I think that the extra water vapor released in cooking puts an extra strain on the unit which has to remove it as it cools the air. There is a bypass channel on our ductwork so we can close off vents to bedrooms and save money while not over pressurizing the supply ducts. If you have a similar feature, you may be able to shut off a few rooms and avoid the whole house getting so hot.

I am sure that low water in your closed loop could also decrease cooling ability, but the piping joints are usually heat sealed and should last practically forever.

I too have wondered if the soil around the pipes gets warmer by the end of summer or colder by the end of winter. My pipes are only 4 feet deep here. I think that moisture has a big part in helping heat transfer, so if the ground is really dry around the pipes, the system might have to run a little longer for the same effect. We are having a drought here too and I can't say that I have noticed the compressor running for an extra long time (our compressor is under our floor in the crawlspace).

It would seem that running a hot water faucet might help your system out, but you would need to shut off your water heater's power or propane so you were not increasing cost via your hot water heater.

Our house is all electric and our monthly bills are about $90 during the hottest part of the summer and $110 during the coldest part of the winter. Spring/fall bills are about $50. We do keep 2 spare bedrooms and 1 bathroom (the whole upstairs) closed off.
 
   / Geothermal heating/cooling question #6  
I do install Geo. From what you stated all is ok. The system should be sized for a set of values normally, 72-75 degrees inside and your average outside temps,( inside and outside design temps) and the heat gain and loss of your house. Change any of these and your system will perform as such.
Detroit design temps are 88 summer 6 winter outside and 75 inside as per Manual J ,what most heat loss heat gain programs use. So you see just by the temps how far away from average you were, then add all the people and door use!

Now if you have a two stage system you may have more capacity.

Your loop will start to loose capacity at the end of the seasons.

Yes your water heater circuit is a desuperheater it may help some in summer but will hurt you in winter.
 
   / Geothermal heating/cooling question #7  
Over heating weather indoors or out doors taxes a cooling system . If you added people or heat (as in cooking ) you added heat load.That said, Units are sized by heat load / heat loss. Everything adds heat load,appliances in operation, people , doors that are opened will also add heat to the home. There's probably nothing wrong with the unit if all is ok now ( after all the heat load is gone) In my opinion, it's easier to heat a home than to cool it
 
   / Geothermal heating/cooling question #8  
Also soil type and moisture content does affect heat transfer. Dry sandy soil can shrink away from the loop piping cutting transfer significantly. Sometimes in soil of this type a soaker tile is installed with the loop to add moisture if necessary .
There are P/T ports on the loop piping by the Geo unit to check pressure and temperatures . With these readings you can calculate GPM and heat transfer.
P/T ports will be little brass caps on the piping going into and out of the Geo unit.
 
   / Geothermal heating/cooling question #9  
the systems i have seen have had a way to monitor the loop water temp: ones system i still say was installed wrong, it was a 6 ton unit, with wells, plumbed in parallel: the water temp would go up a lot on hot days and the system never would keep up: i thought the wells should have been in series: the other way, there was no way to tell if all the water flow was going thru just one well? if you can monitor the water temp, it will tell you a lot about the system and how much change there is with seasons.
heehaw
 
   / Geothermal heating/cooling question #11  
heehaw said:
the systems i have seen have had a way to monitor the loop water temp: ones system i still say was installed wrong, it was a 6 ton unit, with wells, plumbed in parallel: the water temp would go up a lot on hot days and the system never would keep up: i thought the wells should have been in series: the other way, there was no way to tell if all the water flow was going thru just one well? if you can monitor the water temp, it will tell you a lot about the system and how much change there is with seasons.
heehaw

Parallel is right, that's why piping design, flushing, and charging the system with proper antifreeze is so critical. If the system was piped in series the pressure drop through 1000's feet of pipe would make pumping cost prohibitive. All systems monitor the water temp. by freeze stats, temp sensors,low pressure cut out, etc. but not all systems let the homeowner see it, ie. digital read out.
 
   / Geothermal heating/cooling question #12  
I also install geo systems. It could be that the system is just undersized, or you could have ducts in an uninsulated space (attic) and no or insufficient duct insulation, or duct leaks.

If you have a 2 stage system, you may not be hitting the second stage, or there could be a problem with a solenoid. This could be wiring or perhaps a thermostat problem.

The subsurface temp in your area is about 50 deg. This will warm to about 75 deg by summers end if the loop was designed correctly. It is a combo of the ground heating (poor heat transfer in dirt) and an overall ground temp increase seasonally of about 15 deg. Likewise in the winter it will cool below freezing. As stated earlier, try to get a temperature reading on the incoming water line. If it gets too hot, the heatpump should fault. Normally the water temp is not the issue. If the water is 75, it is still quite a bit cooler than the outdoor air which is used on a standard heatpump. Next check the air temp coming out of the unit, close to the unit. It should be about 15 deg cooler than the incoming (room) air. If it is not, have a service tech take a look and check for low charge or other problems.

paul
 
   / Geothermal heating/cooling question #13  
Bill Barrett said:
Parallel is right, that's why piping design, flushing, and charging the system with proper antifreeze is so critical. If the system was piped in series the pressure drop through 1000's feet of pipe would make pumping cost prohibitive. All systems monitor the water temp. by freeze stats, temp sensors,low pressure cut out, etc. but not all systems let the homeowner see it, ie. digital read out.

"if" they had run each set of lines back to the building, so each set could be checked an monitored: but with a parallel system, and the lines all connected underground at the wells: there is no way to know that water is going down each and every well: all the water could be going down one well, an that be why it was heating up to a point it didn't work. they dug them up twice trying to see why the system didn't work, but all they did was double check to make sure they weren't kinked above ground and were connected in parallel: they didn't check to see that water was down an back up each well.
heehaw
 
   / Geothermal heating/cooling question #14  
heehaw said:
"if" they had run each set of lines back to the building, so each set could be checked an monitored: but with a parallel system, and the lines all connected underground at the wells: there is no way to know that water is going down each and every well: all the water could be going down one well, an that be why it was heating up to a point it didn't work. they dug them up twice trying to see why the system didn't work, but all they did was double check to make sure they weren't kinked above ground and were connected in parallel: they didn't check to see that water was down an back up each well.
heehaw

Do they know the flow is low, or are they just low on loop capacity?

You can tell by GPM at the P/T's , if you are only flowing through couple of the wells then GPM will be low. Each pump model can only over come so much head pressure. If they know their pump curve, and the delta P at the P/T ports you know your GPM.
6 ton = 16 GPM or close if your were pumping 16 GPM at your P/T's I doubt you are only using a couple of wells because of head pressure would be to high.
So if it is doing that, the pump must be over sized to over come the head, and your loop design is is not equal length on each circuit.

Do they have 6x150' deep wells? They might not be getting proper transfer.

Parallel circuits connected underground is standard of the residential industry.
 
   / Geothermal heating/cooling question #15  
6 wells, not 100% sure of the depth but over 100ft each i know. they later added on to the building: doubled the size: and had two 3 ton units installed for the new section: and you can hang meat in there in August: while the other side is almost to hot to work in. different installation companies, and i think a different brand unit: the 6 ton unit had to be replaced when it was 7 years old, the replacement doesn't do any better, and is a lot louder: the problem has got to be in the loops, but no one around here has been able to figure it out: system has been in for about 10 years now, and after seeing what kind of problems can come up, anyone that works there that would have considered a geothermal system has changed their minds.
heehaw
 
   / Geothermal heating/cooling question
  • Thread Starter
#16  
I appreciate all the replies - you've been a wealth of knowledge.

Cooling seems to be working somewhat today, but not as strongly as it was working through Friday. It doesn't help that my wife was using the stove for several hours today. The comment about humidity from cooking may well be a factor.

Knowing that the house wasn't built with geothermal in mind, and that both the builder (first owner) and the second owner who we bought it from were a bit shy on cash relative to their horse habits, I wouldn't be surprised if the geothermal system is sized on the small side for the house. I don't know what the wall insulation values are but I think they are very average for 1999. In the winter the geo system supplies all heat until outside temps are below 20F or so and then the propane kicks in more and more frequently (coldest days this past winter had highs around zero with overnight lows in the -teens). The difference is very noticeable - heat from the geo system is only about 5-10F warmer than the indoor temp and has the same humidity, while if the propane furnace is on the heat is 15-20F above indoor temp and painfully dry (there is an air outlet right where my feet go under the desk that I'm typing from).

The statements about standard-book values for my area are very interesting. I think our average soil temp is a bit warmer than 50, at least at a shallow 8' depth, and our average summer high is more like 80 than 88 (Detroit is warmer than where I am). Definitely not too far off though. If the system was designed assuming a summer indoor temp of 75 then we're probably overtaxing it with our preference for 70. I am wondering if between the heat and drought this summer we may have just overloaded the ground surrounding the loop and will have mediocre performance until things cool off in mid September. Oh well, maybe next summer we'll set it at 72 and hope not to have any of these problems. Would it be worth soaking the ground above where the loop is? How many days/weeks does it take for water to penetrate 8' of clay loam?

Can anyone tell me how to detect the ground loop location? The prior owner described where it is, but it's a very vague description. We have called the company that installed the system and asked them (while they were on a service inspection visit) and it sounds like they didn't keep good records of that. Is the piping likely metal or plastic? If plastic, how would you detect it?
 
   / Geothermal heating/cooling question
  • Thread Starter
#17  
More info - we closed the windows last night around dinner time, set the cooling to 70 and waited to see what happened. It *seemed* like it was cooling down and mildly cool air was blowing. But this morning it was warm and stuffy and the temp was still 78, same as it was for most of yesterday. Outside overnight was in the low 70's with nearly 100% humidity.

Our hot water is as hot as it has ever been, so at least that side of the unit is working right (again, as far as I understand we do not have any propane backup for the hot water).

I didn't want to mention earlier for fear of skewing views - when the tech was out a few months ago, he found the system pressure to be low - I think in the ground loop but I'm not sure - but he apparently fixed that (not sure if he had to add fluid or what) and it had been working fine since. He didn't recommend any repairs beyond what he did on the visit. He also mentioned that a circuit board in the unit was melting, but said there was nothing to fix at that time, just to call him back if it fully melted. He didn't say how we would know if that happened, but I'm wondering if we now have the sign?

I appreciate the suggestions on testing it myself but due to lack of expertise and time that's not likely a good option for me. So, here's my question: should we call the repair tech now, or give it another day or two?
 
   / Geothermal heating/cooling question #18  
what "brand" geothermal system do you have?
heehaw
 
   / Geothermal heating/cooling question #19  
Two items come to mind. You stated that it was cool but by morning it was warm and stuffy. Sounds like your evap coil could be freezing up. This can be caused by a low refrigerant charge in the unit, or restricted airflow, such as, but not limited to a dirty filter. Next time it could be worth while to open a cover and see if the coil is iced up when it is not working as expected.

Concerning the loop, the most important thing you can do is to try to get incoming and outgoing water temps at the unit. This will tell you how the outside loops are doing, and how the inside unit is behaving.

The loops should be made from PP plastic pipe, with fusion welded joints on the fittings. If you do not know where it is, it can be difficult to locate. There is some equipment designed to find underground pipes by "listening" to the flow noise, but this is somewhat specialized equipment, not for the average contractor.

paul
 
   / Geothermal heating/cooling question #20  
I'm not technician, but we did have geothermal installed in our home when we had it built in 1999. My guess is either that you system is undersized or inadequate insulation. You talk about your propane system kicking on in the winter below about 20 degrees, but our back up (ours is electric) rarely kicks on even with temps below zero, and then only briefly. Our house has 2x6 framing and is pretty heavily insulated. I do think that the efficiency of the system falls off somewhat as the season progresses but, again, rarely have the backup kick on in the winter. Our cooling system always keeps thinks cool, and we keep it pretty low. We have separate units for the first and second floor, and have the upstairs turned on only at night.
 

Tractor & Equipment Auctions

KBH 25 TON TENDER (A56438)
KBH 25 TON TENDER...
Ford F450 Bucket Truck with Altec AT200A Boom (A56435)
Ford F450 Bucket...
2022 John Deere Z930M (A57148)
2022 John Deere...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
2014 Chevrolet Silverado 1500 Pickup Truck (A55973)
2014 Chevrolet...
Kubota L3130 (A53317)
Kubota L3130 (A53317)
 
Top