2 full 500 gallon tanks only last a week? Seems excessive, what are you heating?

A 16K stand by generator is rated at about 2 gallons per hour at half load. Running full time, that will use around 350 gallons in a week. A larger generator, or higher load will use more. During a normal Winter, I use about 5% with just minimal heat and cooking. That's about 25 gallons or so. Most people have bigger homes and want them warmer than I keep mine, so they'll be using more. Add in the other things mentioned like cooking or heating water for a family and 1,000 gallons won't last long.

And remember, we're not talking about 1,000 gallons. They only load to about 80% or so, or 400 gallons. They don't like them down below about 10%, so we're really talking about 6-700 gallons.
 
   / Getting prepared. #12  
A 16K stand by generator is rated at about 2 gallons per hour at half load. Running full time, that will use around 350 gallons in a week. A larger generator, or higher load will use more. During a normal Winter, I use about 5% with just minimal heat and cooking. That's about 25 gallons or so. Most people have bigger homes and want them warmer than I keep mine, so they'll be using more. Add in the other things mentioned like cooking or heating water for a family and 1,000 gallons won't last long.

And remember, we're not talking about 1,000 gallons. They only load to about 80% or so, or 400 gallons. They don't like them down below about 10%, so we're really talking about 6-700 gallons.
Really?I have a 17kw generac LP installed for the last 10 years,NEVER seem that kind of usage from my 500 gallon LP tanks.Gen. has run 7 days a week 24 hours a day.
 
   / Getting prepared. #13  
Ours runs on propane, so it is super simple. It is always "prepared" and I have a spare 500 gal tank that costs me $54/year to rent.

It is good feeling knowing that you are ready.

Is the reason you (and others) use propane due to not having natural gas already available —- or are there other reasons?

Our heat is already provided by natural gas, so wouldn’t it be best to have the generator also use natural gas?

MoKelly
 
   / Getting prepared. #14  
If you have NatGas and the utility is 100% reliable, you may be better to go that way. Most of the country (at least the rural parts) does NOT have NatGas. At least part of the problem in Texas is that some of the NatGas pumping and supply facilities are shut down due to bad management and lack of readiness.
 
   / Getting prepared. #15  
Is the reason you (and others) use propane due to not having natural gas already available —- or are there other reasons?

Our heat is already provided by natural gas, so wouldn’t it be best to have the generator also use natural gas?

MoKelly

I would definitely say yes Natural gas would be a better alternative but at least here, Eastern Kansas, most gas companies don't run to rural homes. And even some Subdivisions I work in are all Electric. I live rural about 30 minutes Southwest of KC. I have a Heat Pump with propane back up. Would love to have Natural Gas but it is not offered around here to rural customer's.
 
   / Getting prepared. #16  
I would definitely say yes Natural gas would be a better alternative but at least here, Eastern Kansas, most gas companies don't run to rural homes. And even some Subdivisions I work in are all Electric. I live rural about 30 minutes Southwest of KC. I have a Heat Pump with propane back up. Would love to have Natural Gas but it is not offered around here to rural customer's.

Thank you. This helps.

MoKelly
 
   / Getting prepared. #17  
The thing to remember about LP consumption & whole house generators is that they are rarely running at a quarter load, let alone half load. Most get sized to accommodate the largest load demand that might show up. Those max loads are way higher than normal background use. Take a look at your power bill & divide the KWHr. total by the number of days on the bill. Take that number & divide by 24. The result is your average hourly background use. Compare that against the generator max capacity. For us, that is at about a 10% load for our 22kw which was sized to handle a 5 ton heat pump. At a 10% load, consumption is just a hair above 0% load. You can ballpark the 0% load fuel consumption rate by looking at the 1/2 & full load fuel consumption rates. Subtract 1/2 load consumption from full load consumption. Subtract the result from the 1/2 load consumption rate. That will approximate the no-load consumption rate. (This is pretty much the same as taking a chart & drawing a straight line through the published consumption rates (usually 1/2 & full load) to see where it crosses the 0 kw point). For us it is less than 1.5 gph (if memory serves)
 
Last edited:
   / Getting prepared. #19  
My 22 kw never runs at 100%. Ive had a actual fuel monitor on it during a summer outage and it sucked about 1.5 GPH. Over a 14 hour outage. Mind you, the biggest load was my 4 ton ac unit cycling. When that went off output dropped significantly. I feel the biggest problem with whole house systems is undersized generators. A lot of people purchased the 17kw honeywell units sold thru Costco to hook to their houses without any thought to load. You would think a smaller whole house unit would save gas...just the opposite. They continually run at near peak output and suck fuel.

My 22 will run a long time on my 1000 gal tank. And I shut mine off at bed time, and usually part of the daytime if not needed. Unless the wife insists on wanting to quilt in the basement. Must keep wife happy.
 
   / Getting prepared. #20  
That won't help a bit if the roads are closed and the trucks can't get through to deliver. Even two full 500 gallon tanks may only get you a week or so if you're also using LP for home heat, hot water, laundry and cooking.

If you've seen any of Don's posts, you should know he heats with firewood. Like, 53 cords a year or so, lol.

500 gals of propane should last many weeks to just heat your water and cooking, even on top of the generator keeping the fridge and lights on.
 

Tractor & Equipment Auctions

2021 Delta Redirective Crash Cushion 75000 (A49461)
2021 Delta...
2017 Ford F-550 Bucket Truck - 4x4, Powerstroke Diesel, Versalift VST47, 52FT Reach (A51039)
2017 Ford F-550...
Blue-Jet Liquid Fertilizer Applicator (A51039)
Blue-Jet Liquid...
Adams Conveyor (A51039)
Adams Conveyor...
2004 Big Tex 10PI 16ft. T/A Pipe Top Utility Trailer (A49461)
2004 Big Tex 10PI...
2019 Fontaine Traverse HT T/A 48ft Loyboy Trailer (A49461)
2019 Fontaine...
 
Top