GFCI Wiring Issue

   / GFCI Wiring Issue #1  

yooperdave

Veteran Member
Joined
Nov 28, 2001
Messages
1,174
Location
Marinette, WI
Tractor
Tool Cat 5600, LS XJ2025H, Branson 4215HC
Is there someone who can explain how to correct a GFCI outlet in a bathroom which was initially wired to ALSO remove power from the adjacent overhead light if tripped? Home inspector noted as a non-conformance and a safety issue. The overhead lights need to remain energized if the GFCI trips. TIA Yooper Dave
 
   / GFCI Wiring Issue #2  
I built a new house in 1996 that I wired myself. The inspector allowed the GFCI to also remove power from the light as the switch was reachable while in the tub/shower. Otherwise, it would be behind the door
 
   / GFCI Wiring Issue #3  
On the back of the outlet, there should be a 'LINE' and a 'LOAD' connection point. The supply circuit from the panel is installed in the 'LINE' terminal. To continue power to the lamp not controlled by GFCI, attach lamp wires to other terminal of 'LINE', or double up if only one terminal is provided. The GFCI protects the outlet circuit and others that are connected to the 'LOAD' side only.
Hope this helps.
Patrick
 
   / GFCI Wiring Issue #4  
On the back of the outlet, there should be a 'LINE' and a 'LOAD' connection point. The supply circuit from the panel is installed in the 'LINE' terminal. To continue power to the lamp not controlled by GFCI, attach lamp wires to other terminal of 'LINE', or double up if only one terminal is provided. The GFCI protects the outlet circuit and others that are connected to the 'LOAD' side only.
Hope this helps
I am holding a GFCI receptacle in my hand right now and looking at it so I can be accurate. It is a typical unit. In order to power a lamp that is not protected you will need to use a pigtail. This means you will need to connect the power wires to two other wires, such that wires go to the GFCI and the lamp. For example, if you are using wire nuts, the black power wire , another short black wire, and the black wire that goes to the lamp all need to be connected together in the wire nut. The short black wire should be connected to the LINE HOT screw terminal on the GFCI receptacle. The white wire, at least in the USA, should be connected to the LINE WHITE screw terminal on the GFCI. If my answer is confusing I am sure youtube has plenty of videos showing what I just wrote. Your problem is an easy one and I am sure you can wire it correctly.
Eric
 
   / GFCI Wiring Issue #5  
If you get one like this, you won't need pigtails.
(click to enlarge)

IMG_3232.jpeg
 
   / GFCI Wiring Issue #6  
The back of the GFIC outlet should have stickers labeling the line and load side. Put both wires under the line side of the screw to avoid killing the lights. Or get a wire nut and a short piece of wire. Pigtails the 3 conductors together then put the jumper to the outlet. When I’m installing a GFIC I always install it not to protect the down stream wires unless that was the intended design. It saves a lot of dead outlet calls.
 
   / GFCI Wiring Issue #7  
Get an extension cord and run it from the light to a non gfci outlet in another room
 
   / GFCI Wiring Issue #8  
Just remember if you bypass the GFI if there is another receptacle downstream that needs to be protected you will have to add GFI(s) to those outlets.
 
   / GFCI Wiring Issue #9  
Just remember if you bypass the GFI if there is another receptacle downstream that needs to be protected you will have to add GFI(s) to those outlets.
I've always used another GFI for each location as I've found it to be a pain in the butt to go search out the problem when an receptacle doesn't work.
 
   / GFCI Wiring Issue #10  
Get an extension cord and run it from the light to a non gfci outlet in another room
Please don't.
The reason for the spacing of receptacles in the NEC is to eliminate extension cords in residential applications. Extension cords at one time where a fair percentage of the cause of fires and people getting shocked.
 
   / GFCI Wiring Issue #11  
I've always used another GFI for each location as I've found it to be a pain in the butt to go search out the problem when an receptacle doesn't work.

This.

I get it's economical to GFI protect down stream outlets with one. However, it adds an additional layer of head scratching down the road if people get creative with putting switches, receptacles and lights on GFI circuits.

I avoid all that by just putting GFI outlets on the receptacles I want GFI on.
 
   / GFCI Wiring Issue #12  
Please don't.
The reason for the spacing of receptacles in the NEC is to eliminate extension cords in residential applications. Extension cords at one time where a fair percentage of the cause of fires and people getting shocked.

Just cut the ends off the extension cord and wire it in
 
   / GFCI Wiring Issue #13  
I think the wiring is already there. He just needs to move the lamp wire from the 'LOAD' terminals to the 'LINE' terminals.
Patrick
 
   / GFCI Wiring Issue #15  
I've always used another GFI for each location as I've found it to be a pain in the butt to go search out the problem when an receptacle doesn't work.

It should be against electric code to use a GFI inline with circuits that aren’t in sight of each other.
 
   / GFCI Wiring Issue #16  
   / GFCI Wiring Issue #18  
Get a longer extension cord and run it to the neighbors house

Be a lot easier to just pull out the meter and hook some jumper cables across the terminals. Or hammer the ends of some copper tube flat and stick that in for a nicer appearance.
 
   / GFCI Wiring Issue #19  
Good info that I cannot add much to.

Do like mentioned and pull the GFI out of the walls. Move the Load wires to the Line side. If there are more than one set already on the load side....then you need to figure out what one is for the light and only move it.

And as mentioned.....any other outlets that need GFI protection that this outlet was previously doing...will need addressed.

I'd personally start by tripping the GFI, then seeing what/if anything else goes out besides just the light and GFI.
 
   / GFCI Wiring Issue #20  
Actually, while i never have lights and outlets on same circuit in bathrooms, ive never seen a code against it.

unless its a city or local code.

the NEC allows a gfci to be used anywheres within the same room.
 

Tractor & Equipment Auctions

500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
Sakai SV505 Vibratory Roller (A53317)
Sakai SV505...
2012 FREIGHTLINER CASCADIA SLEEPER (A59905)
2012 FREIGHTLINER...
LMC 2-Row Planter BYJ-2F  Stainless Steel Fertilizer Boxes, Ground-Driven (A56438)
LMC 2-Row Planter...
TANK MANIFOLD (A58214)
TANK MANIFOLD (A58214)
2017 Jacobsen 3551 HOURS (A56859)
2017 Jacobsen 3551...
 
Top