The 4 wires being 2 120v hot legs, a neutral, and a ground?
YES
I'm assuming I've got the 4 wires correct as above, where does the Gnd wire from the house panel go in the sub panel? The ground block?
YES> there is typcally a Jumper or a Connector that connects the N Buss bar to the G buss bar, that JUMPER has to be removed, and the Panel Ground is bolted to the sub-panel. the N then is only connected to the Main House Panel's N, NOT to any of the ground paths in the barn/shed.>
Wouldn't this new ground rod ALSO be connected to the ground block in the sub-panel?
YES ground rod & ground in the sub-panel.
3 wires being Hot, Neutral, and Ground?
What are the implications of not having a ground from the main panel going into the sub-panel?
>the implications then are that there can be a potencial voltage differance between the EARTH out in the distant barn/garage and the G recipticals wire ground. < rembember the saying "Ground is not GROUND the earth around," this is an old electricians saying which basically means that if you stick a ground rod into the ground at point A, and run wires 100's of feet away, you can actually measure a + charge between the G wire and the actual earth out away from the ground rod... (there is Resistance in the earth, put in a ohm meter set it to resistance and stick one lead into the dirt, move the other lead as far away as possable and push it into the dirt. you will only measure the amount of resistance from those 2 points to each other. this resistance will change as water levels change and as the dirt comasition changes... wet clay is better at conducting than dry hummus...
)</font>
this is primary reason for adding the ground rod @ an out building and sepperating the N and the G inside the SUB-PANEL @ that location, the codes do not know if the garage is 10 feet away, 100 feet away or 1000 feet away. so reason for seperating the G 7 N is that the N is meant as a return path for power, the G is not. the 2nd ground rod is susposed to tie the two buildings together by Location rather than by RESISTANCE of earth. I'm not 100% sure WHY they want the N & G sepperated @ the sub-panel, to me I think that COULD cause a Floating Voltage on the N vs the 2nd G location IF something were to happen to the G wire that is running between the 2 buildings... (remembering that the G & N are tied together in the MAIN PANEL)
this MAY have something to do with the GFIC requirements, for any building with out a finished floor and or dirt floor or below grade with a concrete floor or with a garage type location where vehicals are stored..... (wet cars/tractors in a garage means higher chance of electrical problems between YOU and the dirt.)
hope that helps.
oh BWT: MY DISCLAIMER
I'm not a pro electrician, I DO a LOT of it and have been doing INDUSTRIAL electricity for years, and have an electronic engr degree but no licenceing, have thought about getting my state licence for electrical and HVAC but just have not had need to do so. I DO keep up on the codes, but only the NEC not any local ones... /forums/images/graemlins/crazy.gif
Mark M