Not workable as a capacity extender IMO due to the variable output, just as a gas saver. My thought is that the fuel savings would be a bonus of having a grid tie system.
On the "backfeeding the inverter issue" I suspect that as long as your total load is low enough that the genset can handle it, the genset will just see a reduced load when the solar panels are producing power.
Most grid tie systems (from what I understand) will not "fire" the inverter and supply power until they see 120VAC @ 60hz, thus only one lockout is needed.
Aaron Z
If the genset has the capacity (and price) to handle the load alone, then money-wise all that can be gained is whatever fuel is saved during a grid outage, and that's only when the solar system is making power. Assuming the solar system is there anyways twiddling its thumbs
You are right about the interlock, only the generator breaker would need to be involved.
I Googled backup generators in grid-tied systems thinking maybe someone has designed a generator to work in that situation. It doesn't look like anyone does.
Some useful articles on the topic:
Generators in Grid-Tied Systems | Home Power Magazine
Q & A: Interaction of Grid-Direct Inverters with Backup Generators | SolarPro Magazine
An excerpt:
But what if an electrical engineer wants to go in a totally different direction? Can the PV system connect to the backup circuit? Will the grid-tied inverter synchronize with the generator output and help support the backup loads? The answers to these questions are complex and entirely dependent on the quality of the generator’s ac output.
It is possible for a PV inverter to interconnect with the stable output of a high quality generator. The inverter monitors the generator’s voltage, frequency and waveform. If the ac waveform is grid quality, the inverter will attempt to synchronize with the generator. If the ac input to the inverter does not dip, sag or surge when the PV system comes on line and starts delivering power to the system, the inverter will remain on line. If the building loads and the generator output are both large relative to the output of the PV system, everything will work satisfactorily as long as the generator does not go out of UL voltage and frequency. However, if the generator voltage or frequency increases beyond the UL 1741 limits, even for a short time as might happen when the PV system comes on line or with a large load shift in the building, then the PV inverter will go off line.
But what if the instantaneous power output for the PV system is larger than the building loads? If there is more power available from the PV system than the total load can consume, the inverter will attempt to put the extra power somewhere, raising the ac line voltage, for example. In this case, when the PV system comes on line, as soon as the voltage or frequency reaches the maximum UL 1741 limit, the inverter will trip off. Unless the total load demand exceeds the instantaneous power output of the PV system at all times, the grid-tied PV system has no chance of staying connected to the generator output.