I'm an electrician and can say the advice you've gotten so far is accurate. b2910 posted that an ohmeter may not provide enough voltage to detect a problem and that is very true. If it does indicate continuity to ground there's no doubt you have a problem or if you don't have continuity from one end to the other. What you really need is a friend or electrician with a megger that will test to ground and between conductors at hundreds of volts.
You need to test it with an electrical insulation tester commonly referred to as a Megger(brand name). It uses a high voltage and measures for current leakage through the insulation to ground Megger. There are lots of different brands just make sure that it is a voltage tester that test at at least 2 times the normal voltage. Disconnect the motor before testing.
You guys both beat me to it. The best means is to megger it. Our megger tests at 1,000 volts. Ask if your friend has one or has access to one. It really is the only accurate portable tester I'm aware of.