Interlock vs. throwing the main circuit breaker for generator powering a house

   / Interlock vs. throwing the main circuit breaker for generator powering a house #141  
Maybe anyone that’s smart enough to grab onto a dropped high voltage line hasn’t had time to reproduce before getting electrocuted. I’m not claiming back feeding is safe or smart but there’s plenty of other hazards.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #142  
In addition most people add up watts and have no clue regarding reactive power. Now they have 4990watts on a 5000W Generator and wonder why the breaker is tripping even through the engine isn't lugging down. All because of that 7000Volt Amp load that they think is 4990 watts.
Far better if the prospective generator purchaser added the amps. Then increase the generator size by at least 150% to have some reserve.

Or you know have a conversation with an electrician when getting ready to install a generator. I have a 6900 w running (8000 w peaking) generator. That was what we needed at the old house. When we wired the new house the electrician and I discussed what would be running during an outage. He told me to make sure the fridge, both pumps on the boiler and the well pump were not running all at the same time. So if I want to go take a shower I just flip off the circuit for the fridge and I am good.

Odds are only one pump for the boiler would kick on at a time, but on a rare case I hear them both kick on at the same time.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #143  
Maybe anyone that痴 smart enough to grab onto a dropped high voltage line hasn稚 had time to reproduce before getting electrocuted. I知 not claiming back feeding is safe or smart but there痴 plenty of other hazards.

The actual hazard is not always that obvious. It is not uncommon to have what caused the blown utility fuse still hanging from the primary line and free of the neutral. If it is blocking a roadway someone could be tempted to remove it, not recognising the hazard that it is on the primary.

I saw a similar hazard several years ago while going to town. A spindly birch was leaning on the 15KV powerline, and the power was still on. I had an appointment but stopped at the neighbour's across the road from it and got her to call 911(as BC Hyrdo requests for a downed line) and to make sure nobody approaches the tree or tried to clear it. BC Hydro had been out and cleared it by the time I returned a few hours later.

Anyhow, we all seem to agree back-feed is dangerous and must be avoided.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #144  
The actual hazard is not always that obvious. It is not uncommon to have what caused the blown utility fuse still hanging from the primary line and free of the neutral. If it is blocking a roadway someone could be tempted to remove it, not recognising the hazard that it is on the primary.

I saw a similar hazard several years ago while going to town. A spindly birch was leaning on the 15KV powerline, and the power was still on. I had an appointment but stopped at the neighbour's across the road from it and got her to call 911(as BC Hyrdo requests for a downed line) and to make sure nobody approaches the tree or tried to clear it. BC Hydro had been out and cleared it by the time I returned a few hours later.

Anyhow, we all seem to agree back-feed is dangerous and must be avoided.

So if you come upon a broken line how are you going to determine which side of the live was energized? Touching a broken line without verifying it’s dead and putting measures in place to verify it can’t be energized is really asking for it.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #145  
So if you come upon a broken line how are you going to determine which side of the live was energized? Touching a broken line without verifying it’s dead and putting measures in place to verify it can’t be energized is really asking for it.

So is working on a verified dead line when somebody backfeeds into it “asking for it”?
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #146  
So is working on a verified dead line when somebody backfeeds into it “asking for it”?

Yes, there’s far too many geniuses with generators to assume that won’t happen. BTW, I have a real transfer switch so I’m not making excuses for myself, but if you think the possibility doesn’t exist you better pay your life insurance and buy some insulated gloves.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #147  
Yes, there’s far too many geniuses with generators to assume that won’t happen. BTW, I have a real transfer switch so I’m not making excuses for myself, but if you think the possibility doesn’t exist you better pay your life insurance and buy some insulated gloves.

Oh, no, I get it. I had a full transfer switch where I had a generator. I don’t have any backup (yet) here.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #148  
So if you come upon a broken line how are you going to determine which side of the live was energized? Touching a broken line without verifying it痴 dead and putting measures in place to verify it can稚 be energized is really asking for it.

That was the point of my post--you cannot determine if a line is energized or from what direction. Thus, assume it is always energized. Although it is deenergized now, it can be energized 1 second from now if someone back feeds with a generator or if the utility personnel decide to close it in one more time to test it. We used to do that 50 years ago but I'm not sure it is as common today. From a lineman's point of view a line is not deenergized until it is grounded. So if the primary conductor is broken they must ground it from both directions before starting repairs.

Your previous post seemed to suggest those who are not aware of the hazard are to blame because they are stupid. If a back feed happens due to a standby generator, that is the real culprit, and it can be out of stupidity or unawareness of the danger created if one does not take the time to learn how to operate it properly.

Those of us with generators have a responsibility to learn how to use them safely.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #149  
So is working on a verified dead line when somebody backfeeds into it “asking for it”?

How do linemen work on dead lines? Do they ground out every line before they touch it? Do they were appropriate PPE when handling it? Sticking a meter only verifies it is dead right now. It doesn't account for anything that may happen in the next instance. I don't know, as I'm not a lineman. All I know is I am required to lock out tag out and verify every circuit I change a light switch, outlet, or ballast on at my employer. What's the procedure for a lineman?
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #150  
How do linemen work on dead lines? Do they ground out every line before they touch it? Do they were appropriate PPE when handling it? Sticking a meter only verifies it is dead right now. It doesn't account for anything that may happen in the next instance. I don't know, as I'm not a lineman. All I know is I am required to lock out tag out and verify every circuit I change a light switch, outlet, or ballast on at my employer. What's the procedure for a lineman?

For a lineman a line is not dead until it is grounded. It is grounded with a cable from the phase(s) to the neutral. As stated above if a conductor is broken they will ground both sides. We also used to (50 years ago) have "HOLD" tags for when we opened a switch and it was hung by the switch. Only the person installing the "HOLD" could remove it or authorize its removal. But that was 50 years ago, they may do it differently now but I suspect it is similar.

That is for primary lines. 240/120v were worked energized with just leather gloves, I'm not sure they do that now.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #151  
Merry
How do linemen work on dead lines? Do they ground out every line before they touch it? Do they were appropriate PPE when handling it? Sticking a meter only verifies it is dead right now. It doesn't account for anything that may happen in the next instance. I don't know, as I'm not a lineman. All I know is I am required to lock out tag out and verify every circuit I change a light switch, outlet, or ballast on at my employer. What's the procedure for a lineman?

Exactly my point. I don’t know what the proper procedure is for linemen and I’ll wager none of these keyboard jockeys do either. I respect the work utility linemen do in all manner of weather a lot more than some here apparently do. Calling them stupid and acting like somebody that gets injured or killed was asking for it is well beyond the limits of human decency. This thread needs to be closed.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #152  
What I have found is several blogs/message boards for utility linemen. To a T, they expect homeowners to be idiots and blame any injuries on poor training by the employer of the lineman or lack of discipline in not following proceedures. One that they refer to in '05 says a homeowner came past them and fired up a generator while the lineman was working on a line he was told was grounded out. It wasn't grounded out, and they never proved any homeowner fired up a generator. The line may have touched something else. Regardless, it wasn't grounded out while he was working on it.
I hate to break it to you,but you are incorrect regarding this story from '05.The line was indeed grounded.The homeowner did in fact fire up an illegally wired in generator in which he immediately had removed prior to the investigation.He also admitted in his deposition that he had turned on the generator that he had wired in himself incorrectly and then removed it.I know this to be 100% accurate,because the lineman who was killed due to this homeowners negligence was my father.I was 15 years old when he was killed.My father had been a journeyman lineman for over 20 years.The homeowner was found at fault.I just wanted to inform you that just because you look up an incident that happened,and think you have all the facts of it,you don't.Today would of been my dad's birthday.I just so happened to Google his name and this forum popped up.I had to grow up with out him and my baby brother had to give me away at my wedding.He has had to miss all my big moments thanks to someone who decided to wire in a generator incorrectly.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #153  
I hate to break it to you,but you are incorrect regarding this story from '05.The line was indeed grounded.The homeowner did in fact fire up an illegally wired in generator in which he immediately had removed prior to the investigation.He also admitted in his deposition that he had turned on the generator that he had wired in himself incorrectly and then removed it.I know this to be 100% accurate,because the lineman who was killed due to this homeowners negligence was my father.I was 15 years old when he was killed.My father had been a journeyman lineman for over 20 years.The homeowner was found at fault.I just wanted to inform you that just because you look up an incident that happened,and think you have all the facts of it,you don't.Today would of been my dad's birthday.I just so happened to Google his name and this forum popped up.I had to grow up with out him and my baby brother had to give me away at my wedding.He has had to miss all my big moments thanks to someone who decided to wire in a generator incorrectly.
I am sorry to hear about the loss of your father. Keyboard warriors are just that; we sit here typing and pretend that we know what we are talking about. Your father died in the real world because a homeowner really was an idiot.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #154  
Every time I read a post about how to avoid connecting a generator properly and safely I cringe. Especially when the person says that everyone in their household knows how to safely do the switch over from the mains to the generator. Oh, and then the poster says they are or used to be a professional who knows better than most folks anyway. Why wait? They should just get it over with and electrocute a family member, friend, or stranger. Because that's what happens all too often. If you can afford the generator then you can afford the minimal cost of the proper switching gear. Sheesh!
Eric
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #155  
I hate to break it to you,but you are incorrect regarding this story from '05.The line was indeed grounded.The homeowner did in fact fire up an illegally wired in generator in which he immediately had removed prior to the investigation.He also admitted in his deposition that he had turned on the generator that he had wired in himself incorrectly and then removed it.I know this to be 100% accurate,because the lineman who was killed due to this homeowners negligence was my father.I was 15 years old when he was killed.My father had been a journeyman lineman for over 20 years.The homeowner was found at fault.I just wanted to inform you that just because you look up an incident that happened,and think you have all the facts of it,you don't.Today would of been my dad's birthday.I just so happened to Google his name and this forum popped up.I had to grow up with out him and my baby brother had to give me away at my wedding.He has had to miss all my big moments thanks to someone who decided to wire in a generator incorrectly.
Please accept my condolences on the passing of your father. I sent you a private message.
MR
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #156  
I've just come across this thread today and have read all 16 pages of it. Some of you come across as being rather arrogant. I do not doubt your abilities nor your interest in doing things safely. BUT, don't forget that in times of stress people tend to forget what they are supposed to do. It is only thru training over and over again that things are done right during stress.

I've flown for both the military and commercial worlds and I've used check lists and I've written check lists. Still, there have been loss of life in accidents in the air because procedures were not followed. There have been fuel tank ruptures in the air because maintenance personnel did not follow procedures on the ground.

For those of you who do not have disconnect or transfer switches, how often do you practice the transfer of power? If you have others in your household, how often do they practice the transfer? I expect the answer is "Rarely". I also know that the transfer of power is not seen as nearly as critical as aircraft operations so will be practiced less and approached with a somewhat careless attitude so the chance of an error is greater. And yet with as critical as aircraft operations are and the training the crews receive, mistakes are still made and people die. So, how much is a life worth? Get the lockout switch! The NEC is there for a reason and gets updated to protect us from new ways we find to put ourselves at risk.

(full disclosure: I've backfed a panel when we were without power for 9 days after a hurricane came thru, so I understand why it's done. But, I've since had an actual auto transfer switch installed along with a whole house generator.)
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #157  
A tree fell and broke our line; the very first thing the lineman did was to connect the lines together with a jumper. That would short out any generators trying to back feed the lines. Not sure if this is new SOP.

I don't run a generator unless it's out for multiple days, it been so many years, I don't remember when I last did it. For the ice storm coming, I've already have signs taped to my back door, Main breaker OFF first. Before I do anything else.
 
Last edited:
   / Interlock vs. throwing the main circuit breaker for generator powering a house #158  
We have a transfer switch in place. It is manual but you can only turn on generator power after you turn off main power. Physically impossible to do otherwise. I cannot imagine doing it any other way (other than automating the process). Back feed is so so dangerous.

Thankfully Indiana looks like it is going to get spared this current winter storm that is going to cover most of the eastern half of the US. However we have all tanks full and generator was test run two weeks ago.

Tractor battery was replaced and she is running like a kitten now. So we are ready.

Oh we did not buy french toast supplies though.
 
   / Interlock vs. throwing the main circuit breaker for generator powering a house #159  
I seldom have long outages. I use extension cords to power anything from my generator. I have never backfed thru my house wiring. I feel very competent that I can open my main and do it, but I don’t.
 

Tractor & Equipment Auctions

Hyster 60 6,000lb Diesel Forklift (A59228)
Hyster 60 6,000lb...
500BBL WHEELED FRAC TANK (A58214)
500BBL WHEELED...
MANIFOLD TRAILER (A58214)
MANIFOLD TRAILER...
SEMI AUTOMATIC QUICK CHANGE FOR MINI EXCAVATOR (A58214)
SEMI AUTOMATIC...
2019 Ram 3500 HD (A56435)
2019 Ram 3500 HD...
18ft T/A Flatbed Trailer (A59231)
18ft T/A Flatbed...
 
Top