with your system running what does your head pressure climb to before tripping out? when the unit is not running your pressures should eqallize and be the same on both sides of the system. i dont believe its a plug in the system, but not able to get rid of the heat in the condenser. not sure how your system is set up but do you have an independant condenser fan
I think it was about 350 (not 100%, but the gauge maxes out at 500psi....and it was about 3/4's of the dials range). What makes me believe it's a plug is after starting......the low side stays at 50 PSI . the high side quickly climbs....then cuts out. Can't think of what else would do that.
System is clean (condensor, filter). The temp out of the vent is ambient.....no change.