The problem would be that the hydrant valve is slightly leaking and the weep/drainage is OK, allowing the leaked water to drain off without filling the riser pipe (except for maybe just a little).
I think shutting off the upstream supply and then monitoring the pressure in the line is your best test method. At least as long as you are pretty sure that the shutoff valve doesn't leak just slightly. Unfortunately in my experience, most valves, with the possible exception of teflon-seat ball valves DO leak just slightly. If the pressure stays solid within 5-10psi over a time period of an hour or two, that would indicate to me that everything is as tight as could be expected.
- Jay
I think shutting off the upstream supply and then monitoring the pressure in the line is your best test method. At least as long as you are pretty sure that the shutoff valve doesn't leak just slightly. Unfortunately in my experience, most valves, with the possible exception of teflon-seat ball valves DO leak just slightly. If the pressure stays solid within 5-10psi over a time period of an hour or two, that would indicate to me that everything is as tight as could be expected.