I am converting a floor standing drill press to variable speed. I bought a KB VFD and a 1 hp, 3 phase motor. The VFD takes a single phase 120 VAC input and produces the 3 phase output. The KB is old school, no keypad programming, instead is a simple speed knob and jumper wire configuration.
I wired it up on the bench and everything functions fine. The motor case is ungrounding as it it still on the workbench. I checked for stray voltage from ground to the motor frame and found 80 VAC. Not my first rodeo so I figured it was capacitive coupled leakage; low current, and would not be a concern once everything was mounted and grounded. To verify I clipped in a 3 ohm resistor from line ground to the motor frame and tested again. The voltage on the motor frame dropped as expected, reading 150 mVAC.
The calculation with 150mV across a 3 ohm resistor works out to 50 mA. I guess that surprises me. 50 mA seems high for a current coming as a result of leakage.
On one hand, if I never checked this I would have grounded the motor frame when it was bolted up to the machine frame; and the VFD has a solid connection from it chassis enclosure to line power ground, so I would have been blissfully unaware.
What is your take? Does the 50 mA seem reasonable? Do I ignore it and proceed to wire it in properly and not look back?
I wired it up on the bench and everything functions fine. The motor case is ungrounding as it it still on the workbench. I checked for stray voltage from ground to the motor frame and found 80 VAC. Not my first rodeo so I figured it was capacitive coupled leakage; low current, and would not be a concern once everything was mounted and grounded. To verify I clipped in a 3 ohm resistor from line ground to the motor frame and tested again. The voltage on the motor frame dropped as expected, reading 150 mVAC.
The calculation with 150mV across a 3 ohm resistor works out to 50 mA. I guess that surprises me. 50 mA seems high for a current coming as a result of leakage.
On one hand, if I never checked this I would have grounded the motor frame when it was bolted up to the machine frame; and the VFD has a solid connection from it chassis enclosure to line power ground, so I would have been blissfully unaware.
What is your take? Does the 50 mA seem reasonable? Do I ignore it and proceed to wire it in properly and not look back?