Generator Need Generator Advice

   / Need Generator Advice
  • Thread Starter
#21  
THANK YOU for all of your opinions.:thumbsup: Sounds like I need to get to work checking and testing. Anymore suggestions are extremely welcome!! I'll keep you posted on the results. Thanks again and keep giving me your opinions!! Sincerely--- Belah :thumbsup:
 
   / Need Generator Advice #22  
Lots of good advice already. I would get a kill-a-watt and check to see that you are getting 60Hz out of your generator. I am not familiar with the Winco but if you are judging the generated Frequency by the tractor tachometer, it could be way too low, which I feel could explain the problems you are seeing. 2200 rpm sounds too low (to be an engine torque peak, where the PTO speed is typically geared for) to me, but I am also not familiar with Kubota.
One other thing to check, your tractor may not be able to put out the HP it is rated for, if there is a fueling problem of some kind. Not sure how to check this short of a PTO dyno check. A generator under load is kind of a dyno, so swapping generators with someone else may prove educational.
Be sure to let us know what you find, thanks.
 
   / Need Generator Advice #23  
The only other serious rat in the feed bin is whether
the brushes are in good condition or need to be replaced
and whether it can be done in the field.:(


A lot of the old JD two lungers with pony motors
and small Oliver 4 cylinder tricycles ran the big
Wincos with no issues SO I am inclined to think
the brushes are the issue.
 
   / Need Generator Advice
  • Thread Starter
#24  
Leonz, This is a brand new generator right out of the box from Winco. The voltage etc. check out fine.
 
   / Need Generator Advice #25  
Check to see if your tractor motor has something called a "torque spring" under the injector pump cover. It appears to be an adjustment (or a maintenance item) that controls the reaction time of the governor. I have a JD / Yanmar motor but what the heck, maybe its worth a chance if these are common systems.

If the tractor is the chief culprit, then find another similar powered one to cross check your powerplant.

The JD manual also mentions injector pump timing as a factor in lazy motor response.
 
   / Need Generator Advice #26  
Leonz, This is a brand new generator right out of the box from Winco. The voltage etc. check out fine.

first: Is the throttle yoke on the Injection pump connected to a threaded rod attachment or is it electric operated?


second: Is the throttle yoke a splined yoke attached to the fuel metering valve which is also a splined fitting on the pump? :confused:
 
 

Tractor & Equipment Auctions

2017 CHEVROLET 2500 HD (A50854)
2017 CHEVROLET...
1998 Ford F800 2,000 Gallon Water Truck (A49461)
1998 Ford F800...
2015 FORD F-250 XL SUPER DUTY TRUCK (A51406)
2015 FORD F-250 XL...
2016 GENIE GTH1056 TELESCOPIC FORKLIFT (A51242)
2016 GENIE GTH1056...
2017 Claas Jaguar 860 Forage Harvester (A51039)
2017 Claas Jaguar...
IH Cub Lo-Boy 154 (A50514)
IH Cub Lo-Boy 154...
 
Top