PTO Generator inadequate for larger HP motors?

   / PTO Generator inadequate for larger HP motors? #101  
Correct, a 2HP or larger motor with a PTO gen.
Depends on the size of the generator. I have 16 kW generator I used on my farm, it will start and then run three 3 hp motors and three 1 hp motors.
 
   / PTO Generator inadequate for larger HP motors? #102  
I got a lesson last week. Our volunteer fire chief has had a long range goal: In his life he wants the fire house, shared by two very small towns to be an emergency shelter for all of the townspeople. His vision included a giant generator big enough that everybody in town could bring any load they could imagine. After 20 years of him asking me to calculate a generator installation of 50, 100, 85, 200 killowatts, he found a donor willing to pay for the full price of a realistic generator. We chose a 14 KW generator. Biggest load we calculated was a 5000 Watt air compressor. My air compressor starts fine on my 10 KW generator, so I expected no problem with a 14 KW machine.

We found the run capacitor bad. Replaced the run capacitor, it started fine with the generator, as long as not much other load.

My seemingly identical compressor at home was bought used, it originally came from a local industrial supply. The one at the fire house came from Tractor Supply. Mine is code G, starting current is 5-6 times full load current. The one at the fire house is code L, 9-10 times full load to start it.
 
 

Tractor & Equipment Auctions

2017 Ford Explorer AWD SUV (A51694)
2017 Ford Explorer...
2013 International DuraStar 4300 Crew Cab Mason Dump Truck (A51692)
2013 International...
2013 International WorkStar 7400 Altec AM650 50ft Material Handling Insulated Bucket Truck (A55852)
2013 International...
66'' root grapple (A53421)
66'' root grapple...
2005 Tennant ATLV 4300 Turf Vacuum (A55851)
2005 Tennant ATLV...
2007 GMC C8500 Altec DL45TR Insulated Material Handling Digger Derrick Truck (A55852)
2007 GMC C8500...
 
Top