I would just use A and C phases and leave B dead. Although you won't be able to fill the panel with breakers, you will have the load more balanced between your two "hots". By connecting the center bus to another you will have the potential to have 2/3 of your load on one of your hots.So my big panel as it turns out, is 3 phase. So in theory, if i bond L2 and L3 and run split phase, i should have all slots active, but if I want to run any 220, i need to make sure I hit L1 with the DP breaker.
The question is do I bond it above the main breaker or below it? Above would be easier, but that would mean the main breaker must be on to bond L2 and L3.
I bought a new panel for my garage, it's powered by a 20a extension cord. If I hook up power to L1 or L2, it works fine, but if I hook the same phase up to L1 and L2, it trips the breaker. My reason for trying that is I wanted all slots to be active. But that didn't work so I'm only running half slots.
The other question is does this old panel have that same sort of protection built in? I'm going to try it with an extension cord tomorrow.
![]()
![]()
![]()
You probably already know this - Even if you do connect all three bus bars (without a 3Ø feed), you will still need to have any DP breaker plugged into slots that get power from the two hots coming in. If, for example, you connect A and B to one hot and C to the other as a feed, you can only get 220v when the DP breaker connects to A & C or B & C. Plugging it into A & B puts both poles of the breaker on the same hot.