i'm not trying to start a war here, but there have been some posts in this thread that have said or implied that these are for light gauge material only, and that they are being misused if you use them on thicker material. i'd contest that is only an opinion, based on the manufacturer's specs. this is the victor page for one of theirs, and it states 1/2" cutting capacity with the included equipment.
Products
i'm not disputing the issue of emptying the tank too fast on thicker material, but like every other dangerous tool, you need to understand how to operate them safely. i'm just not a fan of misinformation for the sake of safety. tell the facts and educate of the dangers.
OK, here is a statement directly copied from Lincoln/Thermadyne's owners manual:
"At no time should the withdrawal rate of an individual acetylene cylinder exceed 1/7 of the cylinder contents per hour. If additional flow capacity is required, use an acetylene manifold system of sufficient size to supply the necessary volume."
Now, here is what that same manual says about acetylene flow rates needed to cut 1/2 inch steel:
Size 0 cutting tip and acetylene consumption rate of 9 to 16 cuft/hr.
With a 10cuft acetylene tank you can safely withdraw at a rate of about 1.5cuft/hr so how can this operation be considered safe? It requires between 5 and 10 times the acceptable consumption rate per hour.
Again, the torch is perfectly capable but not with the mini tanks. The sales material is really very misleading.