"Close" to 60 should be fine for most motors. Microwaves tend to be a finicky appliance, and some UPS units have trouble outside of 58-62Hz.You don’t have a well pump or other 60hz AC motor in your house?
Those certainly care about 60hz being under frequency
It's been a long time since I've run across an A/C induction motor that didn't read 50/60 hz on the motor plate.You don’t have a well pump or other 60hz AC motor in your house?
Those certainly care about 60hz being under frequency
Yep!"Close" to 60 should be fine for most motors. Microwaves tend to be a finicky appliance, and some UPS units have trouble outside of 58-62Hz.
@CalG I've run a WINCO PTO generator for a week more or less straight for 18 hours a day. My only tweak was to put the tractor in 1,000rpm PTO, and then drop the engine speed until the PTO was running 540rpm to save fuel as the tractor had a ton of HP, relative to what the generator needed.
All the best,
Peter
You’re confused. Most American market motors are designed for 60hz.It's been a long time since I've run across an A/C induction motor that didn't read 50/60 hz on the motor plate.
When I first tried running my 3/4 hp deep well pump off my 5k generator, it couldn’t reliably start it. Often just bogged the generator down until a breaker would trip, or I would kick off the breaker."Close" to 60 should be fine for most motors.
One hz? That is one fussy well pump motor.When I first tried running my 3/4 hp deep well pump off my 5k generator, it couldn’t reliably start it. Often just bogged the generator down until a breaker would trip, or I would kick off the breaker.
The generator was factory set at 60hz no load. When I measured, it dropped to 59hz with a moderate load, and 58.5hz when bogged by the stalled deep well pump.
I adjusted the no load to 61hz, no load. During startup there’s a quick drop to 60hz.
Deep well pump starts and runs perfectly now.
Deep well pumps can have enormous starting currents depending on well depth, static water level, and number of check valves
If you need to support, or are interested in supporting, three phase, the surplus military generators in the 5 & 10kW are readily switchable from 120VAC to split phase (120/240) to three phase (not while running!). MEP-802A & MEP-803A, respectively. I know a few folks in NE who support them.I have found modern induction motors to be very tolerant of both voltage and frequency fluctuations.
Most motors in my inventory today, which must be over 16 in number, (though several are 3ph) carry plated ratings for 200-240 volt, 50-60 hz input.
Of course, I'm not going to pull the water pump to assure you of that particular motor plate. But HEY! It's water cooled! I bet it can tolerate a "warm spell" several times per hour.
Just so long as it gets STARTED!
One hz? That is one fussy well pump motor.
5kW is really on small side to routinely start a deep well pump due to the large startup current. Others here have posted about how many pumps and generators get replaced because the generator is too small for the starting surge current.When I first tried running my 3/4 hp deep well pump off my 5k generator, it couldn’t reliably start it. Often just bogged the generator down until a breaker would trip, or I would kick off the breaker.
The generator was factory set at 60hz no load. When I measured, it dropped to 59hz with a moderate load, and 58.5hz when bogged by the stalled deep well pump.
I adjusted the no load to 61hz, no load. During startup there’s a quick drop to 60hz.
Deep well pump starts and runs perfectly now.
Deep well pumps can have enormous starting currents depending on well depth, static water level, and number of check valves
That pump ended up dying. I ran the calculations on my needs and replaced it with an equivalent pressure, but reduced flow rate 1/2hp pump/motor combo, which still flows more than what I need.5kW is really on small side to routinely start a deep well pump due to the large startup current. Others here have posted about how many pumps and generators get replaced because the generator is too small for the starting surge current.
Do you have digital controls on your pump? E.g. a Franklin or an Allen-Bradley?
All the best,
Peter
It sounds great that you were able to work out a pump better matched to your generator and still meet your needs.That pump ended up dying. I ran the calculations on my needs and replaced it with an equivalent pressure, but reduced flow rate 1/2hp pump/motor combo, which still flows more than what I need.
My 5kv generator starts this one no problem. I still stay on the cautious side, and only switch on the well pump during outages when I know the electric stove isn’t in use at the same time. My wife commonly uses multiple burners plus the oven at the same time![]()
Deep well pumps can have enormous starting currents depending on well depth, static water level, and number of check valves
Thanks for the link!I hadn't heard of IMD generators, looked at their site briefly.
Sounds like a decent generator, I didn't see if they were two pole or four pole generators. I prefer 4 poles although their are people on here that either don't think it makes a difference or that a 2 pole is better.
I don't know what size tractor you are going to be using the generator on, but I would not buy a 10KW generator for a tractor. A 16 or 20 kw doesn't cost much more and the heavier mass will help with surge loads and has the capacity if more power is needed.
Even a small tractor can run a 20kw if only 10 or less is being used.
This place has reasonable priced pto generators and you can get them with either a 3.55 ratio or a 4.5 ratio gearbox requiring either 540 pto rpm or 400 pto rpm for the 60 Hz power.
The 4.5 gearbox option would be nice for people with more then adequate hp for their generator and being able to drop to 1700 or 1800 rpm for power production and save fuel.