Radiant Floor Heat Question

   / Radiant Floor Heat Question #1  

TnWV

Platinum Member
Joined
Apr 29, 2008
Messages
589
Location
Liberty,WV - Putnam Co.
Tractor
2003 Zetor 4341 w/FEL, 1970 MF 150, 2012 JD X530
Hey guys, I building a new house that has a full basement (I plan to start a full build thread ASAP). I want to heat the basement using radiant floor heat and have a question about PEX size. The basement is 2100 square feet, so I am thinking 7 loops of 300' makes sense. I can buy 300' rolls of oxygen barrier 1/2" PEX readily. It seems many use 1/2" inch and are happy with it, but I have had a couple of recommendations that I use 5/8" PEX. Problem is, I can only seem to find 5/8" PEX in 250', 500', and 1000' rolls, which makes the layout harder to not waste part of each roll. The basement will not be finished to the same extent as the main living floor, but will be finished enough to be usable for various activities, such as exercise equipment, dog wash room for my wifes dogs, etc. My question is, is 1/2" PEX sufficient? If so, that makes things much easier as far as purchasing the PEX. That said, if 5/8" is the correct size, I will deal with the size rolls I can get. Based on reading other threads here, I plan to staple the PEX to the rigid foam insulation, so it will be at the bottom of the concrete.

Thanks for any insight!

Tony
 
   / Radiant Floor Heat Question #2  
Definitely start a thread about your build. We love threads like that, especially with pictures!!!

I used 1/2". I have 16 loops. My loops are approximately 150'. Bought 1000' rolls. Rule of thumb is 1' of pex per square foot of floor space. You seem to already understand that. Our house/garage is 2,480 sqft. Our system uses a Propane fired tankless heater. We move water at the rate of 2.8 gpm. We are living on our concrete stained and sealed.

In your case with a warm house on top of the basement it will heat very easily. Will take some adjusting to get it so it doesn't overheat. Will also make your house easier to heat because your floors will be the same temp as your basement floor. I would suggest a dual control thermostat that measures air temp and slab temp. This will aid in not overheating.

I can't help with the 5/8" versus 1/2" debate. I've never talked to anyone that used 5/8". It would add gallons of water to the system. But I'm not sure if that's necessary?
 
   / Radiant Floor Heat Question
  • Thread Starter
#3  
Definitely start a thread about your build. We love threads like that, especially with pictures!!!

I used 1/2". I have 16 loops. My loops are approximately 150'. Bought 1000' rolls. Rule of thumb is 1' of pex per square foot of floor space. You seem to already understand that. Our house/garage is 2,480 sqft. Our system uses a Propane fired tankless heater. We move water at the rate of 2.8 gpm. We are living on our concrete stained and sealed.

In your case with a warm house on top of the basement it will heat very easily. Will take some adjusting to get it so it doesn't overheat. Will also make your house easier to heat because your floors will be the same temp as your basement floor. I would suggest a dual control thermostat that measures air temp and slab temp. This will aid in not overheating.

I can't help with the 5/8" versus 1/2" debate. I've never talked to anyone that used 5/8". It would add gallons of water to the system. But I'm not sure if that's necessary?

ovrszd,

I followed your build, and all the other builds that have been posted for the last several years, and I they are my favorite threads. I will definitely start a thread soon, cant seem to stop working on the house long enough. Poured walls are in and the wife and I have worked until after dark most days getting all the drains and gravel in place. Floor will be poured on the 17th, so I have to get everything in place by then.

If 1/2" works well for you, I don't see why it will not for me as well. I will be using a natural gas fired tankless heater in my system. To measure slab temp, due I need to put a sensor in the slab?

Thanks!
 
   / Radiant Floor Heat Question #4  
Tony - IMO 1/2" Pex in the slab over 5/8"... easier to work with, cheaper & if spaced correctly will perform just as good if not better. (5/8" is usually used for larger commercial areas.)

Here in New England we usually plan 8" - 9" spacing with 1/2" PEX, 12" spacing being max or you will wind up with heat striping in the slab (this will also be effected by the Foam Board R-value you use). So for 8" spacing SqFt x 1.5..... 9" spacing SqFt x 1.34 & for 12" spacing SqFt x 1.0 will give you the approx feet in 1/2" PEX tubing. You are 100% correct on 300ft max for 1/2" lop length.

Are you heating the rest of the house with radiant also? If not with what? I see you are in WV but I don't know the climate...

Depending on the construction / building envelope you may have a very small heat load; with a very tightly constructed home with the floors above the basement heated already the basement heat load may be very small. If I was building a new home I'd have a proper Heat Load Calculation done for it, it will take the guess work out of the design for both heating & cooling based on location, construction & materials used... & you can then size the systems correctly...
 
   / Radiant Floor Heat Question #5  
On the projects we have done... For the slab sensor instead of embedding it, they usually put a conduit into the slab in which the sensor can be slid into later.... It allows sensor replacement if ever needed.
 
   / Radiant Floor Heat Question
  • Thread Starter
#6  
Tony - IMO 1/2" Pex in the slab over 5/8"... easier to work with, cheaper & if spaced correctly will perform just as good if not better. (5/8" is usually used for larger commercial areas.)

Here in New England we usually plan 8" - 9" spacing with 1/2" PEX, 12" spacing being max or you will wind up with heat striping in the slab (this will also be effected by the Foam Board R-value you use). So for 8" spacing SqFt x 1.5..... 9" spacing SqFt x 1.34 & for 12" spacing SqFt x 1.0 will give you the approx feet in 1/2" PEX tubing. You are 100% correct on 300ft max for 1/2" lop length.

Are you heating the rest of the house with radiant also? If not with what? I see you are in WV but I don't know the climate...

Depending on the construction / building envelope you may have a very small heat load; with a very tightly constructed home with the floors above the basement heated already the basement heat load may be very small. If I was building a new home I'd have a proper Heat Load Calculation done for it, it will take the guess work out of the design for both heating & cooling based on location, construction & materials used... & you can then size the systems correctly...

dlctcg,

The rest of the house will be heated with a conventional natural gas HVAC system. Exterior walls will be 2x6 with R19 and I will be using ZIP sheeting/tape. House is one story over the basement, so attic will get 24" of blown in insulation. Probably not the tightest house, but will be well insulated overall. Climate isn't too cold here, but we can have single digit temps for a few weeks in January/February at times. IF'300' is max for 1/2" am I better off going down to 250' and 8 loops? Actually, that leaves about 100 sq. ft. left, so maybe 300' is still the best option for even loops.

Thanks.
 
   / Radiant Floor Heat Question #7  
Yeah you will be fine with 300' loops, if the basement is all one zone try & keep the all loops to similar lengths from supply manifold to return manifold...

I know many will say tubing at the bottom of the slab, but none of the contractors we use on our projects do that.... I'll let you do your own research but look at the PDF & do some research... most of our guys are trying to get it closer to mid slab... Just an Idea...

View attachment Common Hydronic Radiant Questions.pdf
 
   / Radiant Floor Heat Question
  • Thread Starter
#8  
Yeah you will be fine with 300' loops, if the basement is all one zone try & keep the all loops to similar lengths from supply manifold to return manifold...

I know many will say tubing at the bottom of the slab, but none of the contractors we use on our projects do that.... I'll let you do your own research but look at the PDF & do some research... most of our guys are trying to get it closer to mid slab... Just an Idea...

View attachment 661737

Definitely one zone for now, not really walling a lot of the basement off, just a bathroom, dog wash room and mechanical room for now. I may add a couple of loops into the attached garage, and that will be on a separate zone.

I will take a look at the PDF and research PEX placement a little further. Thanks for the information.
 
   / Radiant Floor Heat Question #9  
I would put my pex down closer to the bottom, only because if you ever add walls at a later date, you can Hilti-Gun in the sole-plate of the wall to the concrete without fear of nailing a pex-tube. Either way, because of the way radiant works, it is not going to change your heating effectiveness any.

I would also insulate the outer part of the slab, maybe going in by 8 feet or so, but then not insulate the center of the floor. That is where you can really gain some heating advantage by using geothermal heat. Your slab is going to lose heat out against the outer portions of the slab where the cold is located, depending on how your walls are back-filled, but in the center, it will be a constant 57 degrees, or at least in Maine, it is a constant 57 degrees. That is what I did and I got some great results. I also added 400 ton of rock under my slab for added heat sink ability, and the efficiency is staggering.

Last year we lived in a different house, but still owned this one, and I watched the temps in the house. It got down to -7 degrees below zero (f), and the house stayed at 44 degrees. That was with no heat all winter, and no one living in the house. For a 2600 sq foot house to self-heat just by geothermal heat was pretty amazing I thought. It is too uncomfortable to live in for sure, but it means I can leave the house for extended periods of time without worrying about draining water lines and such, even if it is unheated.

As for tube size, I would not worry too much about 1/2 inch or 5/8" because radiant floor heating works by constant, low amounts of heat, unlike baseboard and other forms of heating. You get your heating efficiency by controlling the dwell time in the loops, and not so much by size. But I would add flow-controls to each loop anyway just because you can balance a radiant floor so much easier that way, and adjust that all important dwell time. Get everything right and you will not shock your boiler on the return, and heat your basement really effeciently.
 
   / Radiant Floor Heat Question
  • Thread Starter
#10  
I will certainly be adding walls, and will need to anchor them to the floor. There is a footing under the weight Bering walls and I will not go under that wall with the pex.

Yesterday I used a skid steer to fill in around my plumbing and footings, and converted the whole floor with somewhere between 2-4 inches of gravel. The outer 2 foot is so around the footings was closer to 10 inches. It’s all packed in and ready for vapor barrier and insulation.

I never thought about not insulating the center of the slab, never saw that it any of my research, but it’s definitely an interesting idea. The outside back fill is all river gravel up to where the top soil will be. The over dig is 2 feet or so all the way around. I’ve used 75 tons so far and still working on it.

My next question is, open or closed system? I’m getting varying opinions on that. My initial thought was closed and keep potable water system separate, and will likely do so, but I’ve heard a couple good arguments for an open system. Not having a water heater doing nothing a lot of the year is one, and makes sense. In the end, I don’t want to complicate things any more than necessary.

Floor will be poured on the 17th, and I hope to get it mostly ready this weekend.
 
   / Radiant Floor Heat Question #11  
I did the same thing in my home. 1/2" pex in the basement floor. I use a mixing valve and a Ranco so the water can never get above 90 degrees before the Ranco shuts off the pump. Toasty warm. I did the same in my shop and heat it all with an outdoor wood boiler.
 
   / Radiant Floor Heat Question #12  
I did my 2250 ft2 shop with 1/2” 300 ft loops. Narrower at the perimeter then center. Buried a small tube for temperature probe. Use a bigger conduit.. you can’t push thermocouples very far. Except for startup , the temp variation is very low in and out of floor piping. I have 100 tons of thermo mass in concrete, I just set and forget temperature. ~60 to 70 takes about 24 hours. I put 2” blue foam under everywhere. I put two zones, bath and water room and the rest. Shouldn’t have bothered with two Zones. I use high efficiency water heater( condensing 35 gal ) with heat exchanger and three pumps. Added glycol at first fill. Big mistake. Doesn’t age that well. Lowered heater transfer rate. Only needed if house or heat would be abandoned for a long time.

I measured and took photos of the floor with pex and tapes laid out so we could add room divides and not hit the pex . We used metal stud laid on the floor with short nails and then fit the wood wall studs to pressure the metal to the floor.

Some ideas.

Small pex pipe just delivers less heat per time and takes longer to come to limit. Once it’s there, It runs to make up for losses.
Hole in the center of the insulation would be great if the ground temperature was near your desired operating temp. If it’s below, you will just pump heat into the ground.
 
   / Radiant Floor Heat Question #13  
I agree. I can't logically make the no insulation theory work in my mind.
 
   / Radiant Floor Heat Question
  • Thread Starter
#14  
I purchased part of the insulation yesterday, but no one has enough in one place, so will accumulate the rest by the weekend. Pex will be delivered tomorrow, again, no one local carries more than one or two 300’ foot spools in stock and the pricing locally is insane.

This weekend I will begin the installation and hopefully it goes well since concrete is scheduled for next Friday. I’ll be relieved when it’s done, moving all the gravel has been exhausting. Lumber shows up next Tuesday so it’s just about time to move on to the next step!

Thanks for all the advice! I’ll get to starting a build thread as soon as I can get in the house before 10pm!
 
   / Radiant Floor Heat Question #15  
Is your basement all sub grade or are there many doors and windows. Your heat load will be less the more there is below ground. You say that the upstairs will be "conventional" hvac. You may consider other options. Given that you will have a boiler, I assume, for 2100 sq ft of slab, you could also go with a hydro air system using the boiler for hot water to fan coils. You could do zoning that way. You cooling system would be smaller condensing units to each of the air handlers. Also, with the performance today of mini-splits and the options I would go that way.
 
   / Radiant Floor Heat Question #16  
Home I'm in now has radiant in slab for the walk to daylight basement shop and rumpus room...

It was only turned on once because simply not needed... Rumpus tracks around 66-68 year round...

I have thought the money would have been better spent on radiant under tile dinning, living, bath and hall...
 
   / Radiant Floor Heat Question
  • Thread Starter
#17  
The ground is sloping all around the basement with about 40’ of the back being full daylight with a French door and a couple windows. There will be a 10’ deep porch over the daylight portion.

The radiant is just to make the basement comfortable in the winter without a separate furnace. I probably could have gotten by with a couple wall mount gas heaters, to be honest, but just like the idea of the radiant and figure I might as well give it a go since it cannot be added later.

We have a main natural gas pipeline crossing our property, and get near free gas, so heating with anything electric, like mini splits, is out. If I were doing an electric system, mini splits is likely the way I’d go, or maybe geothermal.

A nice efficient natural gas system should serve me well and cost very little to run, heat wise. I may still run radiant loops under the main floor bathrooms at some point to warm the floors, but that is down the road if I find it’s needed/wanted.

Finished running the 6th pex loop just before dark, will do the last one tomorrow morning before work and hook the manifold up tomorrow evening to test with air. May have to take Thursday off work to get everything finished up. Concrete, pumper, and a crew to pour/finish are scheduled for 6am Friday. Now just have to hope for no rain.

We are building the house our selves and only hiring out the things that we simply can’t do, or just wouldn’t be timely to do, like shingles, drywall, concrete, etc., but I’m hoping after Friday I will have time to start a build thread with pictures and all that. A big load of lumber arrived today and a second is scheduled for Friday afternoon, and will be everything to get me to the top of the walls ready for trusses, so won’t be a lot of rest going on here for a while.
 
   / Radiant Floor Heat Question #18  
Having lived in Europe and spending time in the homes of friends I gained a real appreciation for radiant heated floors... never cold and bathroom space always cozy with something I never thought of almost universal... Radiant Heated Towel Racks... kind of spa living at home with warm floors and heated towels...

Just about all the systems are duel and even 3-way fired... Natural Gas, Heating Oil and Wood.
 
   / Radiant Floor Heat Question
  • Thread Starter
#19  
I definitely hope the heated floors turn out to be enjoyable. We won’t use the basement for full time living but we do have plans to regularly make use of the space.

Last pex run is complete, I’ll tidy up where they come through the floor and install the manifold this evening.

I appreciate all the advice given.
Unfortunately, I probably won’t get to see how well it works until late this winter or the following winter. I hope to be in the house by Christmas, but with the amount of work we are doing ourselves, that could be optimistic, depending on how much help I can round up throughout the building process.

I’ll get a build thread going this weekend, so anyone who wants to follow along can do so.

Thanks!
 
   / Radiant Floor Heat Question #20  
Thanks for the update.

When you start your build thread, link us to it from here, so we don't miss it.
 

Marketplace Items

2019 ALLMAND MAXI-POWER 25 GENERATOR (A58214)
2019 ALLMAND...
2011 KENWORTH T370 (INOPERABLE) (A58214)
2011 KENWORTH T370...
2012 DIAMOND C  40FT GOOSENECK TRAILER (A58214)
2012 DIAMOND C...
2023 VIRNIG RBV50-72" HYD ROTARY BRUSH (A60429)
2023 VIRNIG...
2018 CATERPILLAR 930M WHEEL LOADER (A60429)
2018 CATERPILLAR...
2020 PETERBILT 567 (A58214)
2020 PETERBILT 567...
 
Top