And that's where the NEC gets confusing. There are a variety of exceptions to NEC 225.30, and I'm trying to understand if they apply.
Ultimately, I'll put a sub-panel in if I have to. Just want to make sure that's what is required.
My thoughts are if you go with no sub panel, and I may have missed or be incorrect about some things, you're going to have to at the minimum:
- take up 3 breaker slots in the original panel.
- one single pole breaker.
- one double pole breaker.
- one cable with 2+N+G out to the shed for 110
- one cable with 3+G out to the shed for 220
- anything else that I can't think of.
If you go with a sub panel:
- take up two breaker slots in the original panel
- one double pole breaker in original panel
- one sub panel at the shed
- one single pole breaker at the shed
- one double pole breaker at the shed
- one larger cable with 3+G from original panel to shed
Pros:
- you'll take up 1 less slot at the original panel.
- no 110v cable from house to shed needed.
- room for additional circuits at the shed in the future (big plus for me)
- only 1 wire to run
Cons:
- one more breaker to purchase
- one sub panel to purchase
- may have to purchase an additional ground rod
- heavier feeder wire to shed will cost more.
- two cables have to leave the house and enter the shed
- it may be the only legal way to get 2 circuits to the garage in your area
Anyhow, just some things to think about. It's always nice to have power in an outbuilding. And it seems like I'm always wishing I had an additional outlet on mine.
Good luck with your project.