Shed wiring question

   / Shed wiring question #11  
I think putting 3 outlets on a 20 amp circuit and a second circuit for an HVAC will leave you wanting more in the near future.

If you put a 100 amp breaker box in the shed and run a heavy enough line to feed it from the pole, it will be there and ready for your future projects inside the shed.
 
   / Shed wiring question #12  
I wouldn't bother with a sub panel.
I'd run a 12/3 with grd for 240 v for the AC and a 12/2 with grd for the 20 amp receptacles.

Now you mentioned 3 120V receptacles are they going to be heavily loaded were a single 20 Amp breaker will not be sufficient?

If so then I'd consider a sub panel feed with a 30 Amp two pole on #10 wire or go whole hog and #6 with a 50 Amp,
then add the breakers you need at that panel.
I'm not saying this is the case with the OP, but in some areas it's against code to run more than one circuit to an outbuilding. Two or more requires a sub panel.
 
   / Shed wiring question #13  
I think putting 3 outlets on a 20 amp circuit and a second circuit for an HVAC will leave you wanting more in the near future.

If you put a 100 amp breaker box in the shed and run a heavy enough line to feed it from the pole, it will be there and ready for your future projects inside the shed.
That's similar to what I did for our garage.

I ran a 50 amp 220v circuit from the house to the garage into a disconnect. Then I put an 8 or 10 place box under the disconnect(can't remember off the top of my head). This allowed me to disconnect the garage from the house if I wanted work in the box.
 
   / Shed wiring question
  • Thread Starter
#14  
I'm not saying this is the case with the OP, but in some areas it's against code to run more than one circuit to an outbuilding. Two or more requires a sub panel.

And that's where the NEC gets confusing. There are a variety of exceptions to NEC 225.30, and I'm trying to understand if they apply.

Ultimately, I'll put a sub-panel in if I have to. Just want to make sure that's what is required.
 
   / Shed wiring question #15  
but the shed will be a temporary setup
Define "temporary".
My son built some wooden steps outside a new house in Pa., it was supposed to have concrete when finished.
The house was not considered "finished" and FULLY taxable until the temporary steps were torn out and the concrete steps were poured and inspected by the county.
It took YEARS.
 
   / Shed wiring question #16  
And that's where the NEC gets confusing. There are a variety of exceptions to NEC 225.30, and I'm trying to understand if they apply.

Ultimately, I'll put a sub-panel in if I have to. Just want to make sure that's what is required.


My thoughts are if you go with no sub panel, and I may have missed or be incorrect about some things, you're going to have to at the minimum:

- take up 3 breaker slots in the original panel.
- one single pole breaker.
- one double pole breaker.
- one cable with 2+N+G out to the shed for 110
- one cable with 3+G out to the shed for 220
- anything else that I can't think of.

If you go with a sub panel:

- take up two breaker slots in the original panel
- one double pole breaker in original panel
- one sub panel at the shed
- one single pole breaker at the shed
- one double pole breaker at the shed
- one larger cable with 3+G from original panel to shed

Pros:
- you'll take up 1 less slot at the original panel.
- no 110v cable from house to shed needed.
- room for additional circuits at the shed in the future (big plus for me)
- only 1 wire to run

Cons:
- one more breaker to purchase
- one sub panel to purchase
- may have to purchase an additional ground rod
- heavier feeder wire to shed will cost more.
- two cables have to leave the house and enter the shed
- it may be the only legal way to get 2 circuits to the garage in your area

Anyhow, just some things to think about. It's always nice to have power in an outbuilding. And it seems like I'm always wishing I had an additional outlet on mine.

Good luck with your project. ;)
 
   / Shed wiring question #17  
Got me thinking about how I wired our garage. This is a diagram of the entire setup from meter, through house, to garage. Kinda grainy, but you get the idea.

27D70D97-7466-48B4-9620-139F70B11BAA.jpeg
 
   / Shed wiring question #18  
@rbstern Why penny pinch on this one? Why wouldn't you just put in a sub panel? I would put in a sub panel and future proof your options, as @MossRoad did.

All the best,

Peter
 

Tractor & Equipment Auctions

PTO Generator (A49251)
PTO Generator (A49251)
2019 ALLMAND LIGHT TOWER (A48992)
2019 ALLMAND LIGHT...
2018 Freightliner Day Cab, Detroit Diesel, Auto (A47371)
2018 Freightliner...
78in Bucket (A49251)
78in Bucket (A49251)
Walk Behind Plow (A49251)
Walk Behind Plow...
2016 JLG 2032ES Electric Scissor Lift, 369hrs (A47371)
2016 JLG 2032ES...
 
Top