Spray Foam Insulation

   / Spray Foam Insulation #21  

I read the article and think it's pretty good about the issues with open cell foam and what has happened to houses that use it, but I also think it's a bit slanted in making excuses for those issues. I think that the one thing that we can all agree on when discussing open cell foam is that there have been issues with it and there is a gamble that is taken when using it. The more you search about it, the more you will read both sides of the debate, and for those that support it, the blame is always on the install.
 
   / Spray Foam Insulation #23  
Remind me of an overweight guy that I used to work with that spent $600 on a titanium bicycle seat because it was lighter then his original seat. He rode twice a month and drank beer afterwords. You can spend a lot of money and never see an improvement or return on your investment.
 
   / Spray Foam Insulation #24  
Heat gain and loss is almost exclusively controlled by how well the attic area, or roof, is insulated. This is where foam really shines. Nothing is better then closed cell foam. I would never use open cell and personally think it should be banned from being used in homes. For less money, blown in insulation will give you the same results if you have it applied deep enough to achieve the same R value. It's all about the R value and how much room you have to obtain it. I have 2 feet of blown in Atticat in my house and it's awesome. When I build my shop, I will have a ceiling so I can do the same in there. When I add on to my house, I will have a vaulted exposed beam ceiling with no room for blown in insulation, so I will use closed cell foam for there.
.

So for inside walls and valulted ceilings you would go with closed cell but in a traditional attic you would go with blown in Atticat? I have fiberglass bats between ceiling joists up to joist height and there are a number of gaps from work up there over the years that I am losing heat through. I am wanting to add to or re-do my attic insulation and am curious what you would do in a retrofit, including how to protect the soffit ventilation air path.
 
   / Spray Foam Insulation #25  
If you are building, here is something new to consider, insulated 2x6 studs. Wood only has an R value of 1/inch. You may have R19 in the walls, but with 10% of your wall being studs with only an R value of 6, the overall wall R value is about 12. You need to do something to break the thermal bridge that the 2x6 creates. I have no affiliation with this company, I just stumbled upon them a few weeks ago when researching building materials.
Tstud

1.5" stud every 24" is 6.25% not 10%.
 
   / Spray Foam Insulation #26  
So for inside walls and valulted ceilings you would go with closed cell but in a traditional attic you would go with blown in Atticat? I have fiberglass bats between ceiling joists up to joist height and there are a number of gaps from work up there over the years that I am losing heat through. I am wanting to add to or re-do my attic insulation and am curious what you would do in a retrofit, including how to protect the soffit ventilation air path.

Both Lowes and Home Depot sell Rafter Vents that fit between the Rafters so you will have open air from the vents up past the insulation. https://www.lowes.com/search?searchTerm=rafter+vents

Home Depot will let you use the machine for free to blow in the AttiCat if you buy 10 bags or more.

It takes two people to do this. One to feed the blower, the other to hold the hose up in the attic. Both are easy jobs. Last time we did it was for an addition to our house and my wife fed the AttiCat into the blower while I was in the attic space holding the hose.

Decide how much you want, and figure out where that comes to on the stuff that's up there. If it's a foot thick for R30, mark that on a vent pipe, or AC duct or whatever you have up there. Or two feet for R60. Then just point the hose in that direction and let it build up. Start at the farthest away point and work your way back. Most 2,000 square feet houses will take half a day to spray, so be prepared to be up there for at least that long.
 
   / Spray Foam Insulation #27  
Both Lowes and Home Depot sell Rafter Vents that fit between the Rafters so you will have open air from the vents up past the insulation. https://www.lowes.com/search?searchTerm=rafter+vents

Home Depot will let you use the machine for free to blow in the AttiCat if you buy 10 bags or more.

It takes two people to do this. One to feed the blower, the other to hold the hose up in the attic. Both are easy jobs. Last time we did it was for an addition to our house and my wife fed the AttiCat into the blower while I was in the attic space holding the hose.

Decide how much you want, and figure out where that comes to on the stuff that's up there. If it's a foot thick for R30, mark that on a vent pipe, or AC duct or whatever you have up there. Or two feet for R60. Then just point the hose in that direction and let it build up. Start at the farthest away point and work your way back. Most 2,000 square feet houses will take half a day to spray, so be prepared to be up there for at least that long.
On top of the bats?
 
   / Spray Foam Insulation #28  
Remind me of an overweight guy that I used to work with that spent $600 on a titanium bicycle seat because it was lighter then his original seat. He rode twice a month and drank beer afterwords. You can spend a lot of money and never see an improvement or return on your investment.

....but he looked cool
 
   / Spray Foam Insulation
  • Thread Starter
#29  
I read the article and think it's pretty good about the issues with open cell foam and what has happened to houses that use it, but I also think it's a bit slanted in making excuses for those issues. I think that the one thing that we can all agree on when discussing open cell foam is that there have been issues with it and there is a gamble that is taken when using it. The more you search about it, the more you will read both sides of the debate, and for those that support it, the blame is always on the install.

Yeah, that's my take as well. Like many things I think that it does come down to details of the installation. The closed cell properties make it more robust to installation errors. Improper curing and such could still screw up a closed cell foam job.

It seems that the key with open cell is to keep the dewpoint of the attic air above the roof deck temperature. If that is done most of the time, then the deck will be dry or have time to dry between wet periods and not rot. Besides attic air dewpoint, sun exposure of the roof will be very important to keep the roof deck above the dewpoint. The small air gap between the metal roofing and OSB will help the decking stay warm overnight after daytime heating.

I probably need to embed some thermocouples in the foam touching the OSB and monitor dewpoint in the attic air to decide if there is a problem.
 
   / Spray Foam Insulation #32  
Please pardon my thread hijack, but I have a question related to closed cell foam and air conditioning [ cooling ]. I completely understand the heat saving feature, but is the reverse effect the same ? If a barn space is foamed, will I be able to maintain a cool space benefit ? And would the required thickness be the same?

So, if it's 0F degrees outside on a cloudy day in Winter and I want to have it 65F degrees in my work area from an XXXX Btu heat source [ a delta Temperature of 65F ], I foam to get the required R [if I'm saying that correctly]. So then in Summer and it's 130F up on the roof from the air and sun load, and I want it 65F in the shop (that's also a delta T of 65F) is the insulation value the same, so the cooling Btu A/C capacity is the same? I'd guess the surface temp of the roof is actually higher because of the sun load, so do I need a higher R or more BTU ?

Thanks.
 
   / Spray Foam Insulation #33  
It's the same whether it's heating or cooling. The R value measures the materials resistance to heat transfer. I'm unaware of any material that is different based on which way the heat is moving. However, like you mention, in the summer time the roof is most likely hotter so the thermal gradient is more than 65*.
 
   / Spray Foam Insulation #34  
Yes. Just think of what you have as a first layer with the existing bats. At R19, you need another 6 1/2 inches to hit R30

And as Eddie mentioned earlier you need a "guide" so you can keep track of the depth you are adding.

I used spray paint. I cut off a lathe 3" longer than the depth of insulation that I was adding. Periodically stood the lathe up against a truss brace or whatever and shot paint across the upper end of the lathe. When we started blowing we had purple paint marks scattered around in the attic. I filled until I was near the mark and moved to the next area. Left my paint marks exposed so I wouldn't overfill and waste insulation in spots.

Used the same method when we did my Son's shop addition recently. Takes out the guess work.
 
   / Spray Foam Insulation #35  
My shop isn't insulated and it can become unbearable in the summer. When I built my parents house, they wanted their garage to be fully insulated. They lived in the Sierra Nevada Mountains before moving to Texas and their garage there was insulated, so they wanted that again. I've never done or seen a garage insulated like a house, with R60 in the attick, R13 fiberglass in the walls, double pane windows taped for an air tight seal and insulated garage doors. No matter how hot it gets outside, it's always nice in there. My next shop will be fully insulated, the difference is significant.

How you insulate is up to you, the main goal is to make the walls air tight and the roof R value as high as you can get it. R60 is currently thought of as the point where you are maxed out and wasting material if you add any more. Walls are not as critical as the ceiling is because heat rises and cool falls. You just HAVE to stop the wind on the walls and then it doesn't take much to insulate the walls.
 
   / Spray Foam Insulation #36  
It's the same whether it's heating or cooling. The R value measures the materials resistance to heat transfer. I'm unaware of any material that is different based on which way the heat is moving. However, like you mention, in the summer time the roof is most likely hotter so the thermal gradient is more than 65*.

And it seems the AC mode struggles harder than the heat mode. Not because of R value necessarily but maybe the mechanical process?? For example, if it's 105F outside and you are wanting 65F inside the system will work very hard to do that (40F variance). Versus 25F outside and you are wanting 65F inside the system easily accomplishes that (40F variance).

Maybe someone can explain that or correct my misguided assumptions?
 
   / Spray Foam Insulation #37  
My shop isn't insulated and it can become unbearable in the summer. When I built my parents house, they wanted their garage to be fully insulated. They lived in the Sierra Nevada Mountains before moving to Texas and their garage there was insulated, so they wanted that again. I've never done or seen a garage insulated like a house, with R60 in the attick, R13 fiberglass in the walls, double pane windows taped for an air tight seal and insulated garage doors. No matter how hot it gets outside, it's always nice in there. My next shop will be fully insulated, the difference is significant.

How you insulate is up to you, the main goal is to make the walls air tight and the roof R value as high as you can get it. R60 is currently thought of as the point where you are maxed out and wasting material if you add any more. Walls are not as critical as the ceiling is because heat rises and cool falls. You just HAVE to stop the wind on the walls and then it doesn't take much to insulate the walls.

Our 18x30 attached garage is insulated just like our house. Heated with hydronic floor heat. No AC. Two walls are shared house walls, they are insulated just like the exterior walls of the structure. It doesn't get unbearably hot in the garage in Summer. Easily heated in Winter.

The cheapest thing you can do to any structure that you expect to use year round is stop airflow and insulate.

My favorite saying is, "It doesn't matter what you heat a properly insulated building with, and, it doesn't matter what you heat an improperly insulated building with."
 
   / Spray Foam Insulation #38  
What is the best way to insulate skylight columns in the attic? Would this be a good closed cell spray application?
 
   / Spray Foam Insulation #39  
What is the best way to insulate skylight columns in the attic? Would this be a good closed cell spray application?

What R value are the skylights?
 
   / Spray Foam Insulation #40  
Skylights are like holes in the bottom of a ship. You cannot do anything with them until they leak, then the best thing is to throw them away and put on a new roof.
What is the best way to insulate skylight columns in the attic? Would this be a good closed cell spray application?
 

Tractor & Equipment Auctions

2012 FREIGHTLINER CASCADIA SLEEPER (A59905)
2012 FREIGHTLINER...
2014 Nissan Juke SUV (A59231)
2014 Nissan Juke...
2020 MACK GRANITE (A58214)
2020 MACK GRANITE...
Year: 2015 Make: Ram Model: 5500 Chassis Vehicle Type: Truck Mileage: Plate: Body Type: 2 Door Cab; (A55852)
Year: 2015 Make...
406 (A52706)
406 (A52706)
2016 FREIGHTLINER CASCADIA TANDEM AXLE SLEEPER (A59905)
2016 FREIGHTLINER...
 
Top