I tried to do some load calculations, but obviously do not have any idea of your heat load. I would say that I believe you overloaded the generator (not the PTO hp). The combination of those loads and their cycling on and off with peak start loads requies much more generator than you have. A/C loads tend to cycle on and off. The resistive heat loads are pretty much continuous and I believe place too much of a bias on the generator to let it handle all the cycled loads. I think you were probably running beyond the breaker capacity (at least during peak loading). The breaker which is a heat operated device will take longer to trip (ie handle an overload) at lower temps as some of its heat is dissipiated into the atmosphere. I would hook up all the loads again and put the current meter on the load. You may be suprised. I had a 5500 watt generator for years and their was no way I could run even close to half your load. BTW, what is the rated capacity fo your generator vers the peak load? Also did you have the load evenly spread between the 2 120 v legs?
Andy