I'm hooking up my outside boiler and the trenches are dug, but my question is what gauge of wire do I need? the OWB has 2 I want a cable with 3 so I can ground it to the frame.
 
   / under ground wire help #2  
That will depend on the draw of whatever you are powering. What does the rating plate say on the boiler?
 
   / under ground wire help #3  
My guesses:
Does it have a: Blower? (60-250 watts)
Solenoid for air? (10 watts)
A convenience light? (13-150 watts)
A receptacle (widely variably, call it 180 watts) That's a worst case of say 600 watts, which is 5 amps at 120 volts.
How far is boiler from panel?
For 5 amps a #12 gauge should be able to run a few hundred feet (others with can confirm) with under a 3% (3.6V) voltage drop.

You need to run a 3/c cable so that if your circuit ever shorts to the boiler, there's a low resistance path on the green wire back to the utility's transformer so that lots of current can short into the boiler and the breaker will trip.
 
   / under ground wire help #8  
Well then I'm good at 95'

Depends on the amp draw.

Wire size is based on 2 things. Length, and amps. You have only provided 1 part.
 
   / under ground wire help
  • Thread Starter
#9  
I'll go with #12 that should be good enough to run the pumps and the light.
 

Tractor & Equipment Auctions

Toro Z Master 2000 Zero Turn Mower (A50324)
Toro Z Master 2000...
WB Mower (A50120)
WB Mower (A50120)
2023 Stryker GN3614 36ft. 5 Ton T/A Gooseneck Flatbed Equipment Trailer (A51691)
2023 Stryker...
2012 SOUTHERN 130BBL VACUUM TRAILER (A53843)
2012 SOUTHERN...
2011 TRAIL KING LOWBOY TRAILER (A50459)
2011 TRAIL KING...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
 
Top