Understanding Stray Voltage

   / Understanding Stray Voltage #21  
I am trying to help a neighbor. The cattle were not drinking from a pail with an approved heater. I gave him another brand new heater, same thing. I measured some voltage, from the ground of the receptacle to some tin on the shack leading into the barn.

I installed a temporary cheater plug, removing the ground and for the time being, the animals drank from the pail.

I noticed there was no ground rod at the barn. The barn is fed underground from a house panel a hundred yards away.

We installed a ten foot ground rod at the barn. I was shocked (pun intended) to still see 7 volts between electrical ground and the tin on the building. That tin is apparently in good contact with Earth Ground.

I understand electrical stuff, and have tried reading up on tingle voltage and stray voltage, but I really don't understand what's happening. Or how to correct it. There are Reactor Filters, which are apparently now seldom used anymore and hence no longer made by Hammond, but I understand that even less.

Is there a panel in the barn or is it just one circuit from the house to the barn?

If there's a panel, it should be set up as a sub-panel from the house. The neutral and ground should not be connected together anywhere except the main panel. Is that the way it's set up?
 
   / Understanding Stray Voltage #22  
Is there a panel in the barn or is it just one circuit from the house to the barn?

If there's a panel, it should be set up as a sub-panel from the house. The neutral and ground should not be connected together anywhere except the main panel. Is that the way it's set up?

Can you contact the Electric Utility company and ask for a voltage check and explain the stray voltage to ground .

Look for a pipe line underground or rail road using catalytic voltage to protect the metal . then look at what is in the barn using voltage. Milk parlor vacuum pumps chillers for the milk cooling and water tanks with heaters.

When I was searching for this type of problems even a electric fence will cause stray voltage. One time the farmer put a battery charger on "H" Farmall to have fully charged battery to start on cold morning . it had a one side ground to outlet and he had plugged it rolled over so the tractor was at line voltage. rubber tires kept the circuit from tripping. Next morning first step on tractor gave him a unexpected kick.

Start at main Breaker and if reading voltage to ground keep shutting off breakers until located or remains reading it will be the power co feeding the voltage. High humidity in barns and breaker panels can cause a reading .

If your ground at main continue to have a current flow adding salt deep as can be dug will attract moisture to develop
a power ground to earth.
horses and cattle feel the different potential between the front feet and rear feet. some will not return to barn if shocked by this.
it will surprise you what you find usually totally unexpected
ken
 
   / Understanding Stray Voltage
  • Thread Starter
#23  
Thanks.

It is a two circuit "fuse" panel. The neutral and ground are not connected in that panel.

Do sub panels like that require a ground rod by code?

I had shut off the main switch in the barn and found no difference in the reading. He does have a fencer, but that would give readings on and off in time with the HV o/p, no? Maybe I am missing something with that.

I shuddered when I saw one of those screw in breakers in place of one fuse. I imagined hearing sirens some night and seeing the sky ablaze! I do think fuses were much safer than breakers, except people could do stupid and unsafe things with them. But that's another topic.
 
   / Understanding Stray Voltage #24  
Thanks.

It is a two circuit "fuse" panel. The neutral and ground are not connected in that panel.

Do sub panels like that require a ground rod by code?

I had shut off the main switch in the barn and found no difference in the reading. He does have a fencer, but that would give readings on and off in time with the HV o/p, no? Maybe I am missing something with that.

I shuddered when I saw one of those screw in breakers in place of one fuse. I imagined hearing sirens some night and seeing the sky ablaze! I do think fuses were much safer than breakers, except people could do stupid and unsafe things with them. But that's another topic.

The neutral that is on the line side of that panel, what is it doing on the other end?
 
   / Understanding Stray Voltage
  • Thread Starter
#25  
I suspect it is on the Neutral buss of the main panel in the house. NMW 10/3, House Panel to Barn Panel (2 circuit fused disconnect switch) underground 100 yards unbroken (fairly new cable).

FWIW I get no voltage between neutral and ground at the barn panel.
 
Last edited:
   / Understanding Stray Voltage #26  
I suspect it is on the Neutral buss of the main panel in the house. NMW 10/3, House to Barn underground 100 yards unbroken (fairly new cable).

FWIW I get no voltage between neutral and ground at the barn panel.

Are you getting good voltage phase to neutral?
 
   / Understanding Stray Voltage
  • Thread Starter
#28  
Not sure I measured phase to neutral.

I am still trying to get my head around this. Essentially getting shocked by the ground conductor.

I was thinking though. That fencer. If it had a coupling capacitor neutral to ground or a failed MOV (Lightning Protection) Neutral to ground, it COULD put some voltage on the ground at the far end of a long run IF the neutral was not balanced. And shutting off power at the barn would not stop that, only unplugging the fencer which I don't even know where it is.
 
   / Understanding Stray Voltage #29  
Not sure I measured phase to neutral.

I am still trying to get my head around this. Essentially getting shocked by the ground conductor.

I was thinking though.

An open neutral does weird things. I’ve drawn an arc off an open neutral putting it back together before. Of course that what 12 thousand volt primary voltage, but the same concept applies to secondary. If a phase was rubbing somewhere, you shouldn’t just be getting 7 volts. You would likely be getting 120 volts. Remember a neutral is the return path for stray voltage in a WYE type system. If you have an open neutral, or poor grounds, and are getting 7 volts on the tin, that stray voltage that is generally returned to earth via a grounded neutral, is just waiting for a path to ground. Hence the reason you can measure voltage from the tin to ground.

A capacitor stores voltage and releases upon demand, so it should not be wired into the ground and neutral, and a lighting arrestor is wired phase to ground. They can possibly leak, but generally they just blow.
 
   / Understanding Stray Voltage
  • Thread Starter
#30  
I (believe) I have seen two prong devices that used a coupling capacitor to use the ground afforded by the neutral. I could be very wrong about that.

That switch is very tight and congested, so I don't like the idea of messing with it again. But I wish I had taken some measurements while the three circuits in the barn had the neutrals off.

So, IS a ground rod, code for a sub panel? One, or more?
 

Tractor & Equipment Auctions

2003 Ferris IS1000 52in Zero Turn Mower (A51694)
2003 Ferris IS1000...
Selco V5-HD Vertical Hydraulic Baler (A51691)
Selco V5-HD...
New Skid Steer Attachment Plate (A53002)
New Skid Steer...
Ryobi Sliding Compound Miter Saw (A51573)
Ryobi Sliding...
2018 POLARIS RANGER 570 EFI UTV (A51247)
2018 POLARIS...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
 
Top