John White
Gold Member
Thanks fellows for educating me. Really appreciate the information.
One more thing: your generator will have a breaker that should protect it in over-current situations, but that assumes that your generator is actually capable of delivering full wattage to all outlets/breakers. In other words, if you have a 5000 watt generator, at 120 volts, that is 41.6 amps. If you have two 20-amp breakers, that adds up to 40 amps, and you should be good to go. But let's say you had a 2500 watt generator. That's 20 amps or so, total, at 120 volts. If that generator had two breakers, perhaps they would be 15 amps each, in which case the generator's capacity could be overdrawn without flipping any of the breakers.
The real question, and I don't have an answer to it, is whether it is common practice to always spec breakers with a low enough capacity that the generator can't easily be over-taxed. And, of course, that assumes that the breakers are working properly in the first place! I know I have heard stories of people overloading their generator, so the breakers alone can't tell the whole tale.
I may have just learned something here. Maybe you can help me understand something a bit more. I have a 5500 watt/8250 surge genny. At the moment I can't remember if the 120 receptacles have their own breaker as well as the 240 volt receptacle. The genny just has one toggle switch that says "breaker on/off". Anyhow, If I remember correctly the 240V plug is rated at 30 amps. So if I'm feeding my panel off the 240V receptacle the most I can produce is 30 amps to run house hold things?? I ask because based on your calculations above my genny is rated for 45.8 amps. I saw no where in the specs my genny is capable of 45 amps.
K7LN;2929029That 5500 watts at 240 volts would give you 22.9 amps total. That's for both legs which is where you get the 45.8 figure (120V@22.9A x 2). Your single toggle switch is probably a 240 volt breaker that will handle both legs of 120 volts.[/QUOTE said:That sounds more like it. I think I remember my genny manual stating 23 amps. I just don't understand the "both legs" terminology. I'm gonna check the manual again and I'll post a pic of the power panel of the genny. As soon as my movie is overIts a troy built briggs & stratton model. There is an on and off switch AND a breaker on and off switch though. No visible breakers
That sounds more like it. I think I remember my genny manual stating 23 amps. I just don't understand the "both legs" terminology.
That 5500 watts at 240 volts would give you 22.9 amps total. That's for both legs which is where you get the 45.8 figure (120V@22.9A x 2). Your single toggle switch is probably a 240 volt breaker that will handle both legs of 120 volts.