Hello, I recently was given a 30a-230a dual range Craftmans stick welder. The front says primary 230 volts 50 amps single. I assume this means I will need to wire it to a 2 pole 50amp breaker. What I don't get is that the original 6 foot cord is labeled as 12/3 which I didn't think would handle 50amps so why would I need such a large breaker? For the spikes in current when starting the arc maybe? Seeing wire is expensive I only want to do this once, any thoughts on the guage of the wire? I'm thinkin 8/3 but want another opinion seeing I don't have alot of extra money for overkill. This is all in my basement running about 35 feet. Thanks,
 
/ wiring for welding #2  
The reason is duty cycle. The EL code treats welder outlets a little differently than your used to because the load is not constant like a oven or other appliance.

You could use 10/2 gauge wire for your feed, but 8/2 would be a better choice and would cover you if you got a new welder in the future. This is discussed A LOT on the welding boards like Weld Talk Message Boards - Powered by vBulletin
 
/ wiring for welding #3  
Hi my welder is supplied 60 amps from a 200 amp pnl with a 50 amp plug the plug is A foot from pnl.I run a miller 304 inverter and also a miller vintage 250 wire feeder also a 225 lincoln welder and use one welder at a time with no problem.they do make plugs like arc tite with a metal jacket but are very $$ for higher amp disconnects .I had a electrican wire it up.Sleepy owl:)
 
/ wiring for welding #4  
What does your manual say about it?
I would go by the factory manual first
Jim
:)
 
/ wiring for welding #5  
KubotainNH said:
Hello, I recently was given a 30a-230a dual range Craftmans stick welder. The front says primary 230 volts 50 amps single. I assume this means I will need to wire it to a 2 pole 50amp breaker. What I don't get is that the original 6 foot cord is labeled as 12/3 which I didn't think would handle 50amps so why would I need such a large breaker? For the spikes in current when starting the arc maybe? Seeing wire is expensive I only want to do this once, any thoughts on the guage of the wire? I'm thinkin 8/3 but want another opinion seeing I don't have alot of extra money for overkill. This is all in my basement running about 35 feet. Thanks,

8/3 will definately work...but 10/3 would be OK.
 
/ wiring for welding #6  
MIKE: 10/3 would be safe, but 8/3 would be a better choice for future up-grades to prevent any wire heat-up; use that third wire as an additional ground! Use copper wire only!
LEE
 
/ wiring for welding
  • Thread Starter
#7  
My future is a garage before another welder so I'm ok with not thinking about upgrading in the basement but I will price both ways. I did not get a manual but can order one if needed just haven't got that far yet. I want a bit more power than my little 110v cheapo stick welder, no huge jobs. The 12/3 on the cord still gets me. Thanks for all the replies.
 
/ wiring for welding #8  
machmeter62 said:
MIKE: 10/3 would be safe, but 8/3 would be a better choice for future up-grades to prevent any wire heat-up; use that third wire as an additional ground! Use copper wire only!
LEE

The 12/3 wire on the 6' cord is plenty adequate for six feet; distance and a high AMP load creates heat in a small wire over a longer distance. It's like the difference in flow between a fire-hose vs a long garden hose. Of course you are only pulling a max of 50 AMPS at full power, and 25 AMPS per wire. Hope this helps?
 
/ wiring for welding #9  
machmeter62 said:
The 12/3 wire on the 6' cord is plenty adequate for six feet; distance and a high AMP load creates heat in a small wire over a longer distance. It's like the difference in flow between a fire-hose vs a long garden hose. Of course you are only pulling a max of 50 AMPS at full power, and 25 AMPS per wire. Hope this helps?

Note:: that each wire will carry the whole load not split as machmeter said>

What go's out one wire has to go back the other wire ground shouldden't be carrying any current.

tom
 
/ wiring for welding #10  
The 12/3 on the cord still gets me.
As I said before, It's because of the duty cycle of the welder.

Take a look at the specs of THIS Lincoln welder, the specs are probably very similar to yours. You will see that has has a 20% duty cycle, which is explained HERE.
You can also download the manual from the Lincoln site, that's probably who made your Craftsmen unit anyway.


Also, you only NEED 2 conductor (w/ground) wire not 3. Like 10/2 or 8/2.
 

Marketplace Items

43023 (A59228)
43023 (A59228)
2011 Ford F-350 Service Truck, VIN # 1FDRF3GT8BEA38908 (A61165)
2011 Ford F-350...
2017 CATERPILLAR 120M2 MOTORGRADER (A59823)
2017 CATERPILLAR...
2006 GMC C5500 4X2 BUCKET TRUCK (A59906)
2006 GMC C5500 4X2...
207276 (A52708)
207276 (A52708)
2020 CAT 308 (A53317)
2020 CAT 308 (A53317)
 
Top