Update,
During a phone call to the supplier for the pump and accessories,
I was told that if I went with 115v for the pump, that I need a 30 amp
circuit and breaker. I wasn't aware of this, and was told that I may
be able to get away with 25, but 20 would be not enough for a sumbersible.
(very reputable supplier)
I then went and looked at my electrical setup and found this:
There is a small sub box very near the existing pump setup, that isn't
being used for what it was intended when installed. There is a 50amp
double pole breaker in my main box feeding this box, with 2 large insulated
wires and a ground. (only feeds from 1 leg of breaker) there were a couple
basic 15/20 amp breakers in
the box and were really not being used for anything substantial.
I think this was from an old JenAir type stove. This is looking like a good
possibility for me to power the well , with at least a 25 amp breaker in this
box, and it's right above where the switch and tank are.
I also found an unused 230v wire terminating in the basement, that is only
being used to power the dishwasher now (110) and it is tied into
a 20 amp single pole breaker in the main box. I could easily return
this to a 230 circuit with a new breaker (2 pole) and end up about
10' away from where the pump is.
Neither of these circuits would be included in my transfer pump, so that idea
is going to have to go away. But, I am leaning towards going with the 230v
pump, and then using the extra 230v plug on my generator if I really needed
to power during an outage. (lead cord into the basement and maybe a small transfer box there)
so, if I have the ability to power with 230v, is there any reason to use
115v? other than that box is right there.
During a phone call to the supplier for the pump and accessories,
I was told that if I went with 115v for the pump, that I need a 30 amp
circuit and breaker. I wasn't aware of this, and was told that I may
be able to get away with 25, but 20 would be not enough for a sumbersible.
(very reputable supplier)
I then went and looked at my electrical setup and found this:
There is a small sub box very near the existing pump setup, that isn't
being used for what it was intended when installed. There is a 50amp
double pole breaker in my main box feeding this box, with 2 large insulated
wires and a ground. (only feeds from 1 leg of breaker) there were a couple
basic 15/20 amp breakers in
the box and were really not being used for anything substantial.
I think this was from an old JenAir type stove. This is looking like a good
possibility for me to power the well , with at least a 25 amp breaker in this
box, and it's right above where the switch and tank are.
I also found an unused 230v wire terminating in the basement, that is only
being used to power the dishwasher now (110) and it is tied into
a 20 amp single pole breaker in the main box. I could easily return
this to a 230 circuit with a new breaker (2 pole) and end up about
10' away from where the pump is.
Neither of these circuits would be included in my transfer pump, so that idea
is going to have to go away. But, I am leaning towards going with the 230v
pump, and then using the extra 230v plug on my generator if I really needed
to power during an outage. (lead cord into the basement and maybe a small transfer box there)
so, if I have the ability to power with 230v, is there any reason to use
115v? other than that box is right there.