Running Electric service

   / Running Electric service #1  

ch47dpilot

Gold Member
Joined
Mar 26, 2010
Messages
261
Location
Enterprise Alabama
Tractor
09 Kubota L3400
I'm currently in the process of planning out my home on my 28 acre hobby farm and am looking for ideas on the electric service. The run to the main house is about 650ft and then another 150-200 to the barns. My wife and I would like to have as limited amount of above ground service so that we don't have power poles in our beautiful view off the front porch. I'm interested in what people have done to cover these distances but not had overhead service. I think the only two options would be to run the 200v 400Amp service the full distance, but then everyone I've talked to says I'll probably get to much voltage drop. The other option is to convince the power company to run the high voltage service underground and the put the transformer about 50ft from the home and then only 100ft to the barns. If anyone has a different idea or worked with the power company providing the high voltage service underground let me know what I should do.
 
   / Running Electric service #2  
ch47dpilot said:
The other option is to convince the power company to run the high voltage service underground and the put the transformer about 50ft from the home and then only 100ft to the barns. If anyone has a different idea or worked with the power company providing the high voltage service underground let me know what I should do.

In our area that is exactly how it would go - high voltage to a good location, then a transformer on a concrete pad. Every day occurrence here. Have you spoken with your local utility co?
Mike
 
   / Running Electric service #3  
The 240/120 line can not run too far because of voltage drop. With 650 ft you will have to run a higher voltage line back to within a couple hundred feet and then a transformer. The closer the better to limit voltage drop and flicker when motors start on compressors etc.
As suggested by Mike talk to your utility they can help you. Depending on their service regulations they may allow UG free. It could be more expensive for them to run overhead if they have to cut right of way to get back to your place. Maybe you can dig the trench for them and get a cost break. If you do your trench and also back fill after they install cable keep it free of rock. Rock against cable is not good.
 
   / Running Electric service #4  
We're having a house built right now that is about 2,100 feet from the road. Power company will lay high voltage cable to a transformer box about 50 feet from the house. They pay for the cable, I pay for the excavator.
 
Last edited:
   / Running Electric service #5  
the electric co. was more than happy to run my 200' under ground. no poles to look at or ice on the lines. they instaled a transformer around 50' from the house a sq. box just siting on the ground. this was in 93 and only charged .05cents per ft. i ran a under ground line to the barn from the braker box in the house . with no problems.:thumbsup:
 
   / Running Electric service #6  
We have underground electric for our house run to a transformer on a pad 600 feet from the road. Our barn is 200 feet from the house. Our barn has 100 amp electric and the wiring for it is underground. We have had this set up 12 years with zero problems. When ice storms come, like the one predicted tomorrow, the underground wiring is comforting to have.
 
   / Running Electric service #7  
I believe the matter of who pays for what varies state to state. In Arkansas I am building a house and have 700' of conduit buried for Entergy to install high voltage line to a transformer that will be outside my house. Entergy would have provided 800' of overhead line for free, including 3 poles. I have to pay the difference in cost of underground service. I installed the conduit to save on cost. My cost is around $900 on top of trenching and conduit.

The service line from the transformer to the meter is much more expensive than the high voltage line so I placed the transformer about 20' from the house.
 
   / Running Electric service #8  
im an electrical contractor located in Idaho. You can feed a house located 600 feet from the transformer, but you have to severely upsize the feeder wires. For example, if the transformer was 50 feet from the house, a 4/0 alum feeder would work. but at 600 feet, to maintain the same voltage drop, you may need a wire size of 500 MCM aluminum. i didn't run the exact figures, but i did a shop reciently that was 500 feet from the 400 amp service and thats how its calced out. id check with the utility . here they charge $10/foot to relocate the transformer. 600 ft = $6,000. i think 600 feet x 3 runs of 500 mcm wire would be cheeper...but not by much. also, it depends on your loads. if you use a heat pump system, a large voltage drop to your residence will probibly cause the lights to dim when the system kicks in. If you never expect to have large loads ... maybe you wouldnt notice any difference. ..but i personally would not risk it. What i tend to do with new properties (AND I DID ON MY OWN) IS TO LOCATE A 400 AMP meter with 2 - 200 amp breakers and a small sub panel equil distance between the house and the future shops. set this 50-60 feet from each. then have utility place transformer next to this meter.then you have your electrician run the 60 foot feeds to the house (200 amp) and 60 foot feeds to shop. I usually insta;ll my meter section with the small subpanel so i can add future things later...like wells, water trough heaters, etc. hope this helped
 
   / Running Electric service #9  
im an electrical contractor located in Idaho. You can feed a house located 600 feet from the transformer, but you have to severely upsize the feeder wires. For example, if the transformer was 50 feet from the house, a 4/0 alum feeder would work. but at 600 feet, to maintain the same voltage drop, you may need a wire size of 500 MCM aluminum. i didn't run the exact figures, but i did a shop reciently that was 500 feet from the 400 amp service and thats how its calced out. id check with the utility . here they charge $10/foot to relocate the transformer. 600 ft = $6,000. i think 600 feet x 3 runs of 500 mcm wire would be cheeper...but not by much. also, it depends on your loads. if you use a heat pump system, a large voltage drop to your residence will probibly cause the lights to dim when the system kicks in. If you never expect to have large loads ... maybe you wouldnt notice any difference. ..but i personally would not risk it. What i tend to do with new properties (AND I DID ON MY OWN) IS TO LOCATE A 400 AMP meter with 2 - 200 amp breakers and a small sub panel equil distance between the house and the future shops. set this 50-60 feet from each. then have utility place transformer next to this meter.then you have your electrician run the 60 foot feeds to the house (200 amp) and 60 foot feeds to shop. I usually insta;ll my meter section with the small subpanel so i can add future things later...like wells, water trough heaters, etc. hope this helped

Our house was built in 1999. We bought it four years ago. I have no knowledge of the cost or size wiring that was used to feed our transformer that is 600' from the road. We have geothermal here. Pretty much a super sized heat pump. We have no issues with the lights dimming when the geothermal kicks on. This set up works and works very well. I wish I could contribute with the cost of this but I can not.
 
   / Running Electric service #10  
I suspect by now it's clear that you need to talk to your power company and see how things are done in your area.

I have a high voltage line for 800', then a 100' run to the house.

When I had a big track loader in here, I cleared a path through the woods for the high voltage drop, it was about 10 feet wide. When the power company showed up to price the options of buried vs. arial, they were about the same because they just had to run a trencher for buried but would have to take out more trees to clear a path for the arial. The arial had the potential of having more maintenance cost down the road. There is a preference for buried even though it cost more. So an hour of track hoe time saved a bunch of money and I got buried.

I do have to cut any trees that start to grow in the 10' easement. This keeps roots from trees away from the buried line, and allows access if there is a problem. Where I used to live, we had a buried line in a subdivision that got blown when there was a lightning strike out at the pole where the line when underground. The key concept here is that you'll need to keep the easement open and you should factor that into your site and maintenance plans.

Pete
 

Tractor & Equipment Auctions

Case-IH 160 Puma (A57148)
Case-IH 160 Puma...
2014 AMERITRAIL LAY FLAT HOSE TUGGER TRAILER (A58214)
2014 AMERITRAIL...
McFarlane 4030 Reel Disk (A59814)
McFarlane 4030...
UNVERFERTH 330 8 AND 1/2 INCH EXTENSION STUB TUBE WELDMENT FOR FRAME (A55315)
UNVERFERTH 330 8...
Pull-Behind Batwing Rotary Brush Cutter Attachment (A59228)
Pull-Behind...
Landoll 876C Soil Finisher (A59814)
Landoll 876C Soil...
 
Top