.you cant just put the transfer switch ahead of the meter
Oooo and the transfer switch goes after the meter not in front of the meter...
.you cant just put the transfer switch ahead of the meter
Well from my standpoint, I cannot in good conscience sell a client the idea that i can simply add the transfer switch to his loaded out panel and he should expect it to be trouble free automatic transfer without a hitch. What happens if the power fails in winter and he forgets to turn off the hot tub heater (automatically keeps hot tub to 102 F) and forgets to turn off water heater and emergency back up heat unit.....
You can see where i am going with this. I have to guarantee my install for 2 years
On your split panel do you only put load enough to not overload the gen set.. ?? 10kw gen.. you only load to 8kw in your panel.. Just trying to understand not hounding you,,
Your not hounding me at all. The panel i install allows up to 125 amps on the generator portion of the panel. I simply place up to the generators rating worth of circuits (actual tested load) and leave the rest on the non-generator portion of the panel. Then anyone can change circuits as needed within the panel, and not have to re-fed a separate gen panel later on.
I try and do the install the cheapest LEGAL way. I guess some other people just want to do it the cheapest way. I have tried to just install the transfer switch in the past, and the inspector made me install a separate generator panel rated for the generator. Now if the geherator IS large enuf, i will simply install the transfer switch.
Local or state inspector.??. If a transfer switch is rated for 100a say and the generator has a breaker rated for 50a. What reason would the inspector give for not installing it.. ??
Ooo the Generac 200a transfer switch has a load shedding feature for ac/heat pumps units and hot tubs,, so no worry about overloading gen set,,
So what alot of people do are buy a 50 amp generac (home depot special) auto start generac generator and they want to power their 200 amp panel. I tell them we cant power the heat, water heater and stove with this unit. So i have to install a smaller 50 amp panel next to the 200 amp panel (if theres room) with a 100 amp auto transfer switch between the two. I power the new 50 amp panel from thew house panel, then i have to re-run all the circuits that the owner wants to run off of the generator to the new panel. 6 hours later, hes up and running, with alot of drywall repair.
...
Or, i pull out the old panel and install the new panel (1-2 hrs work) add a feed to the generator and I'm done. The new panel is a legal split bus panel that will LEGALLY allow the installation of the lower amperage generator as you can move circuits to balance the load to match generator output.