Well, it seems you have had your question already answered.
Disclaimer: I am not an electrician. I just know enough to be dangerous:laughing: But I have a good understanding of electrical and residential wiring, enough to tackel anything I need, but again, I am not an electrician.
I was going to say 115V minimum, but you already got that answer.
There are a coouple of things that could be causing you issues. First (and you say you are on it) is to check what you have at the MAIN panel. It could be low from the get-go. My mains are usually 121-122V:thumbsup:
Second, you probabally have TOO long of a run with TOO small wire. 12ga is the standard for 20A circuits. BUT, when you start to go over 100ft, the voltage drops is what gets ya.
I am not sure of your lay-out, but you say this is the farthest outlet, is their a MAIN 240v panel in that building, or only a 120 line running to it? May need to upgrade and put a panel in that building. Just thinking out loud.